Just up too late. Nothing exciting happening, I'm an engineer, after all.
As a side note, that E limitation appears to carry through to 2012 IRC and with the switch from Table 602.3.1 to 602.3(5) the footnote is gone.
Should anyone be interested in a quick link, here's the
2015 IRC, Chapter 6, third printing.
Mike Mike said:
Are you saying within the IRC "there's maybe other provisions elsewhere for anchor bolt spacing due to the lateral (soil) load"? I spent many hours digging thru the IRC at this point, pretty sure there's nothing in here, but let me know if you see something.
Eh, well, no. I didn't find anything special about lateral loads on the sills, there's some fine tuning you could do on your calculation but it is highly unlikely to alter a 1,800% overstress. I just feel compelled to mention, in case that's coming from a design somewhere, but the refinements appear to increase the allowed load so it's conservative as is. I didn't read Stephanie's article, I just saw that comment about load path when I was trying to find it for discussion...
Mike Mike said:
Floor trusses are specifically permitted by 2024 IRC R502.12 and require engineered design regardless of span. You can't get more "in the middle of two prescriptive designs" than that. If you were EOR would you not allow your clients to use floor trusses?
Touche. Agree they are pretty clearly sandwiched between a prescriptive stud and a prescriptive foundation. But isn't that engineering by somebody else? The truss engineer? I'm not too sold one becomes a "full" EOR on a project just by doing a tall stud wall, you know? I'd expect at least 4 out of five dentists would allow floor trusses without batting an eye, similar for roof trusses.
Source: 2018 International Residential Code. (actually the image is from the 2020 Minnesota Residential Code, but I don't think there are any changes.)
You could probably read that to permit a sandwich of an engineered design between two prescriptive systems, but it's got some (mild?) peril to it, but the peril we're talking about specifically is the wall connection at the top of a soil-retaining foundation wall and that's not happening due to the wood truss...
One would like to think a too long span for the truss will have bearing/crushing issues with a 2x4 that would prompt a question, but then again, I've seen that exact defect on an engineered three story building with an occupied roof and a penthouse, all in wood. So, probably not.
Going to the top of your post -
1 - Some sort of "gateway" check would seem in order, since there aren't engineers on these items, and it's difficult for them to a) make the call when it comes to snow load, seismic load, and b) they could then know (the building officials as well) where to expect engineering. Or how to design so as to avoid it.
2 - That or add "engineering required" for the floor attachment beyond where the 6' sill spacing stops working, with some inclusion of possible dead load friction or say a 25% increase to the stresses..? I feel like some states have revisions in that area to provide additional bolts.
Source:
2020 Minnesota Residential Code
That would be the kind of modification to propagate "upwards"?
3 - What about bringing back the footnote on F
b and E? Took them what, 6 years to add the superscript on the 1.6 x 10
6 psi and change the "by" to a 'x' indicating multiplication? Like as a starting point (although maybe it came back after 2015, I haven't looked that far, so much (unnecessary) reorganization and renumbering .... so many adds) In the northern areas, we tend to see 2x6 studs for insulation so the 2x4 parts of the table are of less relevance to us up here so they get less scrutiny. The table is kind of funky anyway, to me it's a bit backwards, but nonetheless. Somewhere an "engineering required" would be nice to see in that table. If they'd just stop rearanging things and moving sections all the time, that would surely help.
4 - Another perfect opportunity for "engineering required" in a table, which would send folks retreating to eliminate the need for engineering and go back to more standard spans. We'll ignore the 25% decrease for clinched nails for now, but wouldn't a double shear connection tend to provide more than a 25% strength increase? I've not tried to calculate it out, when I get stuck with this situation I use hardware that's been load-tested (cough Simpson cough).
How about (A) - Delete all that garbage for light gauge stud and joists and punt it to the light gauge people to publish their own bloody standard a la the WFCM? Do the light gauge studs calculate out better as somebody put them into the code? Why did they sandwich all that light gage garbage between two wood framed sets of provisions (Floors, Decks), that's just a bad decision from the go.
Mike Mike said:
Yes, there are a few refinements that could be made to my basement wall calc, but it doesn't change the conversation
Granted. I just have to point out the little stuff.
1. R507 is for decks. I'd eliminate those at your peril.
Lateral Loads Generated by Occupants on Exterior Decks, Parsons, Bender, Dolan, Woeste, Structure Magazine, Jan 2014. As an engineered design, code calls for it to be "designed for lateral loads" (not really a quote, sorry), without any guidance.
2. Single top plate is possible without engineering in both codes, I think.
Mike Mike said:
Top plate nailing requirements of table R602.3(1) lines 13 and 14 are extreme overkill and can be reduced or deleted.
3. Which part is excessive? I suppose cheaper with fewer nails, sure, nothing dramatic, though, and would the framer actually look at that or just do it per "code minimum" like they've done forever. The splice (1422 lbs?), last I checked, is the same in the two codes, unless the options in the IRC are different. If we're comparing R602.3.1 and Chapter 23, they tend to be pretty similar. The IRC doesn't control a top plate splice location so it's presumably in the worst case location between two braced wall panels at the ends, it's a collector/drag strut, and the nailing is probably unchanged since, say, 1926.
Item 4 isn't an IBC/IRC difference, it's an Engineered versus not difference.
Mike Mike said:
Are you saying you would be okay with specifying 1/2" bolts at 6' to brace the top of your basement wall just so long as you noted on the detail that the connection was selected from the prescriptive requirements of IRC only. Would you include a note requiring the owner or contractor to hire an engineer to verify the connection?
Never been in that particular boat, so to speak. The last situation I had that was reasonably close was a precast plank and a cast in place retaining wall with a house above it. So the sill bolt doesn't really do much as to the restraint of the top of the foundation wall, there. The next closest I have is a concrete floor with a masonry wall under it from let's say 1940. The sill anchor isn't doing much there, either.
That situation is where you should probably flag the issue and if it's not your design, write so explicitly. That's more of a before you issue drawings item, however.
This is a wide ranging discussion, even in the U.S., we've gone from liability, standard of care, prescriptive design, etc. As Greenalleycat mention, who gets sued isn't constrained by "I followed the code" as an absolute defense, though it does usually help the defense. To briefly divert, something like vibration, in the U.S. isn't even in the code, it's "governed" by some research and publications published by various suppliers and standard setting organizations but they aren't generally code requirements. You'll find calculation guidance for steel framing, wood framing, and steel joist framing, but to my knowledge these are guidelines for appropriate practice (i.e. standard of care) but they are not code in the statutory sense. In that situation for a suit against a design professional, there usually needs to be another similarly licensed design professional's report indicating negligence, deviance from a design standard, etc.
The very first words in this thread are "The IRC...." This is the Residential code that most of the U.S. functions under. That's what we're talking about.
As to the horizontally spanning masonry foundation wall, is there a requirement for a bond beam anywhere in the IRC that might provide that, or are we expecting the mortar bedding in tension to do something or ladder reinforcing (if required?).