A few thoughts after reading through the threads:
1. It would seem "eyeball" inspections are not enough to determine whether or not a building is in grave structural danger especially since all components are not visible, including the foundation elements. Even if an inspector or engineer felt collapse was immanent, they would still face the reality of condemning a building that is considered prime real estate in the middle of its useful life. That is far different than condemning an abandoned building. The backlash of peers, officials, owners, agents, and politicians could cost you your career. We are always told "buildings don't just fall down in America". So who wants to be the first to say "Well this one is about too!"
A solution, which is already being used on site, could be to monitor buildings using modern day surveying equipment. Every new building could be surveyed upon completion and every 10 years afterward. The deflections and loading conditions could be recorded and cataloged for comparison throughout the structures life. Old buildings could be evaluated the same way only the task would be more difficult with no starting point to compare too, however still useful. This would provide scientific evidence if there were a problem and would protect inspectors and engineers from having to make judgement calls. Given the 3D laser technology today, this is more achievable than ever.
2. A building made of thin two-way flate plate floors on columns using frame action and minimal shear walls to resist shear is not a redundant or robust structure. They are used for cost savings, speed of construction, and floor height. The design is governed by punching shear and when one goes where does it stop. Whether the slab punches first (dropping onto the floor below and doubling the unbraced length of the column) or a column buckles or is damaged (doubling the span of the slab and pulling on all of the adjacent columns), it seems progressive failure is inherent in this type of construction until it runs into a wall or change in framing that provides support.
3. The design load requirements by ASCE should be examined thoroughly after this for condos or commercial space over parking garages. As of now the loads are 40 psf for residential spaces, 100 psf for lobbies, corridors, and egress paths, and 40 psf for parking garages? I understand that parking garages have been value engineered to nothing and that 40 psf is pretty close to actual loading and that no residence is ever likely to see anywhere near 40 psf...even if they have tile over tile over tile floors, but the end result is the basement and first floor levels being pushed to their limits on a routine basis (not including dynamic loading and vibration, which are ignored) while the upper floors hardly ever see 20psf. Then try explaining to someone how the pool deck and lobbies should be the most robust slabs designed for 100psf when they are empty most of the time and yet cars are packed into the garage like sardines in the same picture...
A solution could be to increase the loading requirements for parking garages to 100psf located under residential/commercial spaces, especially towers (with no LL reduction). This would result in thicker slabs, more reinforcement, bigger columnns, and more foundation elements such as pilings. In addition more concrete cover could be specified to protect against damage from vehicles (Murphy's Law?)
4. Structures located in corrosive environments should be designed for corrosive environments.
5. That D-ring detail is scary as hell! Some poor crew is supposed to dangle themselves off the side of this building hanging by horizontally epoxied bolts into a 40 year old column made of questionable concrete? Count me out. Haven't there been studies showing this is done improperly 9 out of 10 times? Aren't horizontal and overhead applications only supposed to be done by a certified technician? Why not clamp a steel bracket around the column? Something that can be inspected for safety.