Calif_Eng
Civil/Environmental
- Aug 20, 2019
- 10
I have an 11 foot wall to support a road next to a creek in an alluvial floodplain in very poor soil. The geotech engineer is not allowing any bearing, only 200 psf in slip friction for nine feet of sandy strata beginning two feet under the lagging for nine feet in depth (13-22ft). Under that its liquefiable until you get down 40 feet. With the LFRD STR I condition I have lateral loads of 1.35EH + 1.75LL + 1.25DC. I was planning a soldier pile single tieback wall, W12x53 r=1.25 @ 8 ft centers, but the vertical resistance factor of the soldier pile for slip friction is .55 which results in 1.25DC exceeding the .55* 200psf slip friction resistance on it's own. The tieback exerts additional downforce on the soldier pile. Alternatives: I can't do RSP as it will get into the creek and environmental review will reject. Intuitively, I'm very leery of a deadman at an angle down to provide additional resistance. About forty feet down the geotech hit some decent material but they only went two feet into it so we'd have to do more geotech. Then I maybe could do piles and and double tiebacks. Any thoughts?