I was pushing laterally on a 20'Hx25'W Great Room wall the other day to show the builder how weak the wall was. With only me pushing on the wall at about 4' to 4.5' from the floor, you could easily see it moving in and out. The wall is almost all windows and doors. It was framed with 2x4 syp wall studs. The upper half is mostly windows and the lower half is windows and doors. It passed city inspection I am told but that may not be true.

There are several framing issues that created the problem, but in shoving on the wall, I told the builder I cannot push horizontally on the wall more than about 1/3 my body weight and that was minor in comparison to the wind the wall was supposed to resist (5,000 lbs or more). The builder claims people can push more than their body weight and used someone bench pressing as an example. I know the bench pressing is not applicable to this.

My question is mainly, how hard can someone push laterally from shoulder level against something when they have nothing bracing them from overturning themselves. I used 3' spread of my feet and 4' to 4.5 for the distance to my shoulder and that is where I get my 1/3 approximation. Does that sound right? (3'/2)xP = 4.25xH ---> H = .375P -----> Ballpark 1/3 your weight.

RE: What magnitude of minor lateral force on Great Room wall makes it shake

The limit will be how high the friction is with the floor, though I suppose if there is high friction with the wall you might go higher.

What might be more valuable is to put a floor weight scale against the wall and see how hard the builder can push. If it is less than 5,000 pounds and the wall moves a noticeable amount then that indicates there might just be a problem.

RE: What magnitude of minor lateral force on Great Room wall makes it shake

(OP)
While the friction would account for sliding, overturning has been my problem. My feet do not slide, but I overturn at some force because my only stability is my body weight and a moment arm equal to half the spacing of my feet.

RE: What magnitude of minor lateral force on Great Room wall makes it shake

W*e = Fmax*h
Fmax = W*e/h

W = weight of person
Fmax = maximum force against wall
e = horizontal distance from c.g. of W to c.g. of foot furthest from wall
h = height of horizontal force Fmax

BA

RE: What magnitude of minor lateral force on Great Room wall makes it shake

Even if you could push with 500# it is 1/10 the wind load.
Looks like a problem.
Get a scale and ruler on a stand, flex the wall, record load and deflection.

= = = = = = = = = = = = = = = = = = = =
P.E. Metallurgy, consulting work welcomed

RE: What magnitude of minor lateral force on Great Room wall makes it shake

Since you figured it out, why did you ask?

RE: What magnitude of minor lateral force on Great Room wall makes it shake

20' tall 2x4. Not sure how that would work even if an interior wall with only 5psf wind load.

RE: What magnitude of minor lateral force on Great Room wall makes it shake

(OP)

Quote (Ron247)

My question is mainly, how hard can someone push laterally from shoulder level against something when they have nothing bracing them from overturning themselves. I used 3' spread of my feet and 4' to 4.5 for the distance to my shoulder and that is where I get my 1/3 approximation. Does that sound right?


3DDave- I asked if what I figured out sounds right.

RE: What magnitude of minor lateral force on Great Room wall makes it shake

Quote:

My question is mainly, how hard can someone push laterally from shoulder level against something when they have nothing bracing them from overturning themselves.

Isn't that a question?

Maybe ask only one question if want the answer to only one question.

I told you how to exactly determine that value - you do own a bathroom scale, don't you? You have access to a wall. You could have found out in the time it took to complain about my very correct answer.

RE: What magnitude of minor lateral force on Great Room wall makes it shake

2x4 framing is a little light for 20' height... I'm not a 'wood guy' but I've done tall walls in wood, 20' high and they were 2x8@16, including wind loading. Remedy might mean adding and securing another 2x4 stud wall to the face of the existing; the solution may not be easy.

With a coef of friction of about 0.5, I suspect the push would be about 100 lbs max. If on an angle, maybe a little more becaused of the apparent 'added' weight.

Was the wall built from any drawings? or did the contractor just 'build it'? The use of a scale would give a good approximation of the load.

Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better?

-Dik

RE: What magnitude of minor lateral force on Great Room wall makes it shake

Not only are 2x4s light for the height, but they would likely be spliced as well. Wood splices can be flexible and problematic.

I don't know too much about the residential code, but there might be some prescriptive designs in the code for which to compare your wall.

RE: What magnitude of minor lateral force on Great Room wall makes it shake

No more 20' trees? ponderThey used LVLs for the ones that I was involved with...

Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better?

-Dik

RE: What magnitude of minor lateral force on Great Room wall makes it shake

Fmax*h = W*e

image edited




BA

RE: What magnitude of minor lateral force on Great Room wall makes it shake

I looked into this once. Professional rubgy players and sumo can sustain about 100% of body weight as lateral force. Average humans top out closer to 70%.

----
just call me Lo.

RE: What magnitude of minor lateral force on Great Room wall makes it shake

(OP)
Lomarandil, do you mean they can create a force of 100% while standing still or while moving? In my case, I would be using the standing still value. I can see that squatting down would increase your ability since the moment arm reduces. In the case I am talking about, BAs sketch is very close.

dik-I think the contractor just built it. I doubt the plans were detailed.

RE: What magnitude of minor lateral force on Great Room wall makes it shake

(OP)
They are full length 20' 2x4s. They may be from a local mill and may not even be graded. This is not the first one I have run into. Last one was replaced with a steel tube frame. One of them I ran into was two 10' walls placed on top of each other to make the 20' wall. It shook very easily too.

Owner was concerned due to movement so that is why I went out. They saw it move with a moderate wind. At this stage, the builder has to get his own engineer involved since he thinks it is ok. I do not know who he will get but I am confident it will not work.

RE: What magnitude of minor lateral force on Great Room wall makes it shake

There would be an Fmax at his feet limited by coef of friction.

Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better?

-Dik

RE: What magnitude of minor lateral force on Great Room wall makes it shake

Can you introduce a couple of 2x10 or whatever pilasters? may be the easiest fix.

Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better?

-Dik

RE: What magnitude of minor lateral force on Great Room wall makes it shake

It looks like most of these calculations assume only body weight, but there ought to be stances that can produce more than body weight, although not necessarily for very long. A weightlifter could potentially a 600-lb force for a clean and jerk and 1000-lb for a bench press or squat.

TTFN (ta ta for now)
I can do absolutely anything. I'm an expert! https://www.youtube.com/watch?v=BKorP55Aqvg
FAQ731-376: Eng-Tips.com Forum Policies forum1529: Translation Assistance for Engineers Entire Forum list http://www.eng-tips.com/forumlist.cfm

RE: What magnitude of minor lateral force on Great Room wall makes it shake

You could apply an impact factor of 2 to the static body weight (BW) force, so 2 x 0.33BW = 0.66BW. That would be more in line with the typical force Lomarandil suggested.

Shouldn't really need calculations to win this argument with the builder though... If a wall is visibly moving under moderate wind or human pushing, isn't that objectively unacceptable for conventional US construction "by inspection" ?

RE: What magnitude of minor lateral force on Great Room wall makes it shake

In my experience, if you can shake it, it is not ok. With a lot of windows, that wall would likely need to be 2x8 construction. Might be easier to show the builder a quick calc. with code C&C wind loads on it.

RE: What magnitude of minor lateral force on Great Room wall makes it shake

Calculations aside, I'm pretty sure I've never seen a wall that I could push laterally and detect any noticeable deflection.

If someone short of a World's Strongest Man competitor can move the wall enough to see it, that's good enough proof for me.

RE: What magnitude of minor lateral force on Great Room wall makes it shake

I agree that the wall has problems. No question.

But in terms of putting a number to the force, why not put a bathroom scale between your hands and the wall? I would try to find an analog version, digital ones make you wait until it is at equilibrium sometimes..

Those of you at home today could probably give the OP the rule of thumb he is seeking (% of body weight while standing at a normal stance pushing on a wall) in a few minutes..

All of this assuming bathroom scales work vertically, but I think they should (accurately enough for this anyway).

RE: What magnitude of minor lateral force on Great Room wall makes it shake

I confess I already did the bathroom scale test this morning. Partly curious, partly procrastinating from my real job.

Static push was ~35 lbs, shoving hard was ~70 lbs. I weighed in at 155 lbs and was wearing socks thumbsup

RE: What magnitude of minor lateral force on Great Room wall makes it shake

Is this 2x4 20ft tall wall braced at all for out of plane loading? If not, you've exceeded the allowable code prescribed slenderness using 2x4 framing at 20ft, nevermind the lateral forces involved. Refer to AWC NDS section 3.3.3, I get a slenderness of 68.6.

RE: What magnitude of minor lateral force on Great Room wall makes it shake

Some versions of IRC technically allow crazy tall gable walls as long as they are nonloadbearing,and contains very little as far as full-height king stud requirements. I do not do much residential design, but I had to chase down the requirements for a friend a while back and I was stunned how flexible of a wall was allowed.. No doubt they need a beefier wall, but If you have a sharp contractor, you may have an uphill battle from a code perspective. However I think even these (woefully inadequate in my opinion) requirements call for at least 2x6 studs..




RE: What magnitude of minor lateral force on Great Room wall makes it shake

Quote (bones206)


I confess I already did the bathroom scale test this morning. Partly curious, partly procrastinating from my real job.

Static push was ~35 lbs, shoving hard was ~70 lbs. I weighed in at 155 lbs and was wearing socks
Sounds about right to me.

I would think the absolute upper bound would be what the person can overhead press, not bench press. 200 lb is a lot for a recreational athlete. 300 lb is a lot for almost anybody. The world record clean and press is about 500 lb iirc. Take those times the cosine of about 45 deg.

RE: What magnitude of minor lateral force on Great Room wall makes it shake

(OP)
Several have mentioned the use of scales. I am 2 states away from home in a motel and even at home, I think we threw the scale away because it quit working and have not bought another one yet. Not sure how rotating it 90 degrees affects accuracy but probably close enough.

Thanks bones206, at least that gives a starting point. 1/3 of body weight woudl be 50. You hit between 35 and 70.

RE: What magnitude of minor lateral force on Great Room wall makes it shake

If bathroom scales are used, the weight of the scale has to be included in the equation. This would give a somewhat exaggerated value for Fmax. (See below)

Available friction underfoot would be another consideration.

W*e + Wbs*d = Fmax*h

BA

RE: What magnitude of minor lateral force on Great Room wall makes it shake

Quote (the weight of the scale has to be included in the equation)


I think you are using a scalpel where an axe would be more appropriate.

Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better?

-Dik

RE: What magnitude of minor lateral force on Great Room wall makes it shake

I think it's important to note in BA's diagram the answer to your overturning question. Without e, there's no force against the wall. Try it now, standing vertically see how much purely horizontal force you can apply to the wall while remaining vertical.

Also this whole scenario is interesting. In my opinion, if the builder finds an engineer to qualify this without changes, feel free to report them to the board.

RE: What magnitude of minor lateral force on Great Room wall makes it shake

Quote (Without e, there's no force against the wall.)


Without e, there's minimal force against the wall, I suspect. pipe

Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better?

-Dik

RE: What magnitude of minor lateral force on Great Room wall makes it shake

(OP)
I rotated my hips and put one foot against the base of the wall and the other foot was about 3' away. Other than that I was abotu what BA depicts.

I doubt an engineer will sign off on this. The ball is in his court. Find one that will, let them do their calcs and submit them for review. At 10 psf wind and 500 square feet compared to maybe 100 lbs max a person can push.

RE: What magnitude of minor lateral force on Great Room wall makes it shake

Even sumo wrestlers could not exceed their weight unless they were wearing special shoes with a static friction value greater than 1.0 on the floor finish.

BA

RE: What magnitude of minor lateral force on Great Room wall makes it shake

Superglue on the Sumo wrestler's bare feet.

Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better?

-Dik

RE: What magnitude of minor lateral force on Great Room wall makes it shake

While I completely agree that the wall is not adequate by the sounds of it, I do feel that everyone is missing one key item when it comes to maximizing the horizontal force you can apply on the wall. That is the vertical friction between your hands and the wall.

Rather than pushing the wall over with a purely horizontal force, one would push both horizontally and up, essentially becoming an axial member. This does two things, it eliminates the overturning problem and it also increases the friction force between your feet and the floor (by increasing normal force). This will allow you to exert much more force on the wall, which will only be limited by your strength or the frictional resistance between you and the wall or floor.

RE: What magnitude of minor lateral force on Great Room wall makes it shake

Quote (dauwerda)

While I completely agree that the wall is not adequate by the sounds of it, I do feel that everyone is missing one key item when it comes to maximizing the horizontal force you can apply on the wall. That is the vertical friction between your hands and the wall.

Rather than pushing the wall over with a purely horizontal force, one would push both horizontally and up, essentially becoming an axial member. ...
I agree. I think we can set a reasonable upper bound as I described above. The maximum axial force in the person (LOL) is how much he or she can overhead press. For people who are pretty strong, that's about 200 lb. Take that and multiply it by 0.707 to get about 140 lb maximum horizontal force.

I'd guess an average man can overhead press no more than 120 lb, so that's about 85 lb maximum horizontal force.

RE: What magnitude of minor lateral force on Great Room wall makes it shake

Why would you need to overhead press it? Your legs are much stronger than your arms. Start with your arms straight out (or use your shoulder and eliminate your arms all together) and use the muscles in your legs to increase the axial force.

RE: What magnitude of minor lateral force on Great Room wall makes it shake

Still have to maintain the axial load in the arms and spinal column.

I can't hold a lot more above my head than I can overhead press. It becomes a stability problem. LOL. I guess I'm making the leap that this is about all anybody could muster.

RE: What magnitude of minor lateral force on Great Room wall makes it shake

(OP)
In my case, my arms were horizontal. It makes sense that pressing upwards with your hands while pushing horizontal will increase your vertical stabilizing force and would be related to wall friction value and how hard you are pushing horizontal.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close