Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Lateral Pressure of Flowable Fill concrete against a basement wall

Ron247

Structural
Jan 18, 2019
1,187
I have a situation where a house transitions from a crawl space to a basement. The crawl space area immediately adjacent to the basement wall was not backfilled and the first row of interior piers for the crawl space are very close to the 8'+ drop-off. There has been soil sloughing off over time near the piers.

I told the Owner of the possible remedies, and they decided they want to fill the area with flowable fill. I have suggested doing it in 3-4 lifts and letting each lift set up before installing the next lift.

I have questions:
  1. Am I correct that once the concrete cures, the lateral form pressure from that pour is no longer present against the concrete basement wall other than any lateral soil pressure from the embankment that may have "shifted" during the pour?
  2. I recommended placing plastic across the bottom and up each side at least equal to the total pour height to help prevent liquid/flowable fill from seeping into the finished basement area due to the pressure. Is that reasonable to expect? It looks like the concrete wall sets on stone, not a concrete foundation.
  3. I did not design the concrete wall but it was a manufactured product that was installed by the supplier. I am having owner's get confirmation from supplier it is designed for lateral soil loads of the expected height. Is there more I should have them confirm?
  4. The finished floor above is wood. I have recommended well ventilating the crawl space during curing to minimize effects from the heat and moisture from the drying process of the flowable fill. Is that a reasonable expectation.
  5. Anyone ever do this before, and if so, what problems did you encounter?
Any advice is greatly appreciated.


1747065937568.png
 
Replies continue below

Recommended for you

I have run into this before but have never had to come up with a fix. I assume flowable fill because access is limited?
 
Yes, not easy to bring in soil or stone. Owner likes the "cleaner look" of concrete. I filled a large area before with flowable fill but it was a large crawl space some guy excavated to make a basement. He died before he ever finished. Years later his wife was trying to sell the house. Difference was, I was pouring against a wall of dirt, not a concrete wall and the floors were carpet or ceramic tile above. We still ventilated the area.
 
1. I would think that the pressure from the wet concrete would still be there after curing. Maybe over time it could lessen due to shrinkage but seems like there is no physical mechanism to relieve the pressure if everything is still in contact. Multiple lifts is a good idea and will lessen the overall lateral pressure due to not having the full height liquid all at once.
3. Is there a way to figure out how the concrete wall was attached to the foundation?
5. I've done this before, but in a commercial application. I specified a maximum unit weight for the mix when liquid, not sure how that would go in residential.
 
The wall does not look like it is attached. In fact, it appears to me that without the backfill, the wall is free to move laterally towards the embankment. Below is a sketch of a typical precast basement wall like this project.

1747069991489.png
 
So best option pour a footing for the CLSM to keep the wall base pinned. Likely the precast wall was designed with soil loads on that side and relies on the floor slab and flooring to provide bracing. Investigate light weight fill that is a sand cement mix with a foam agent.

Calculate the pressure created by the wet fill and compare against typical soil pressure. When it hardens it will have unconfined strength. Use foam board to lessen the residual stress on the existing wall. If really concerned about lateral pressure between lifts use ICF as a bond break and after each lift cut the ties out. This in the end will leave a gap between the fill and existing wall.
 
  1. Am I correct that once the concrete cures, the lateral form pressure from that pour is no longer present against the concrete basement wall other than any lateral soil pressure from the embankment that may have "shifted" during the pour?
I agree with this. I would be propping the basement wall until the grout is set as I think the pressure in the wet phase will be substantial
  1. I recommended placing plastic across the bottom and up each side at least equal to the total pour height to help prevent liquid/flowable fill from seeping into the finished basement area due to the pressure. Is that reasonable to expect? It looks like the concrete wall sets on stone, not a concrete foundation.
100%. This is a must-do IMO. Right now that area is well ventilated. You are going to be providing an easy path for moisture to get through into the back of the basement wall. There is a serious risk IMO that this fix creates a significant issue that leads to dampness and mold.
  1. I did not design the concrete wall but it was a manufactured product that was installed by the supplier. I am having owner's get confirmation from supplier it is designed for lateral soil loads of the expected height. Is there more I should have them confirm?
There's design, then there's construction. How confident are you that both have been executed the same way? Also, it may be designed for those lateral loads, but normally the lateral loading would be applied before other structure is built around it i.e. install wall -> backfill (applies pressure) -> build framing above etc. You're now loading it last which means that any forces & displacements from the backfilling will be transmitting into the rest of the structure. Can it handle that? Again, I'd recommend propping the wall to do your best to mitigate any loading/movement of the existing structure
  1. The finished floor above is wood. I have recommended well ventilating the crawl space during curing to minimize effects from the heat and moisture from the drying process of the flowable fill. Is that a reasonable expectation.
I think you'll need to mechanically vent the subfloor for a while (I couldn't put a time on it. Maybe Google can give you some drying curves). In general, is the subfloor well ventilated?
  1. Anyone ever do this before, and if so, what problems did you encounter
I have encountered a surprising number of subfloors that look basically exactly like your scenario there, and sometimes they have had previous (or current) moisture issues to be dealt with. However, they are normally left open (your current state), built a timber pole retaining wall, or have standard filter cloth/drainage chip/drainage pipe behind the wall. I have not encountered one with your proposed solution of mass concrete. I am concerned it's not the right solution. My thinking is: your issue is moisture in the soil. Your solution should not focus on stabilising the face, it should focus on getting the moisture out. Then stabilise the slope at the end, if you need to - that soil will probably stand vertical if dry.

Where is the moisture coming from, and can you control that? If not, I think your grout solution runs the risk of worsening the problem, not making it better.
 
Have you considered any potential settlement risk of existing footings associated with the fill placement?

The bulb of influence of the new fill would extend to below at least the soils below the first line of piers. If there are any compressible layers seeing new stress from your hunk of concrete you could have some minor movements.

I'm in the middle of a project where the want to do this for a substantially larger footprint (~6' of fill in a ~20' x 20' square). I requested they get a soils guy to comment on any potential settlement risk on the existing foundations due to the fill placement, and I'm still waiting to hear back. Your application is much smaller so maybe not as much of a concern.
 

Part and Inventory Search

Sponsor