I am in charge of designing the metal panel for a project in a 140mph wind zone. The metal panel is going to be supported by lt guage girts at 4’-0” o.c. I am currently trying to design the attachment of the panel to the girts. I can use 2 types of fasteners, a joint fastener (#14 T3 screw) and a “back fastener” (Fab-Lok). Joint fasteners are always used to join two panels together. When the loads become too great for a single joint fastener, a back fastener is used. I have the allowable capacities for both joint fasteners (464#) and back fasteners (153#).
On an equivalent 2’-6” wide panel I have a suction of 731#. Is it appropriate to add up all the capacities of the fasteners that act on the 3’-6” wind panel and make sure they are greater than 731# (1 side fastener and 2 back fasteners 770#) or do I have to apply the wind loads to each fastener based upon their tributary area (apply 1 side fastener and back fasteners at 6” o.c.)?
On an equivalent 2’-6” wide panel I have a suction of 731#. Is it appropriate to add up all the capacities of the fasteners that act on the 3’-6” wind panel and make sure they are greater than 731# (1 side fastener and 2 back fasteners 770#) or do I have to apply the wind loads to each fastener based upon their tributary area (apply 1 side fastener and back fasteners at 6” o.c.)?