I have a 18" auger cast piles with 7 #8 vertical rebars. The vertical rebars extend upto 25'-0" based on the deflection/moment curve. The total length of the pile is 60'-0". The piles are subjected to considerable uplift and moments (100k and 90k-ft strength loads). I am designing the pile as a column and 7#8 bars work for combined tension and flexure.
My question is,
1) Is there a minimum spacing requirement between the vertical bars for auger cast piles? Can I go with 8 #8 bars in 18" pile?
2) I have a #8 vertical bar at the center of the pile going all the way down. Typically this bar is used to resist uplift. In my case I am using the main vertical bars to resist uplift in combination with flexure (column interaction). Based on the soil report, I need 15'-0" of pile length to resist 100k of uplift from skin friction. The vertical bars I have extends 25'-0" which is beyond the required length of the pile to resist uplift. This means I dont need to extend the rebar all the way down to the pile to resist uplift as the uplift reduces down to zero at 15'. Any concerns with the way I am approaching the design? I will still keep the #8 center bar going all the way down from detailing perspective.
My question is,