Minimum Flexural Reinforcement ACI 318-19 8.6.1.1 for a very thick slab

oengineer

Structural
Apr 25, 2011
732
I have a foundation slab that is 4'-11 thick (the total dimensions are 14 ft x 14 ft x 4'-11" thick) & I am wondering if Minimum Flexural Reinforcement ACI 318-19 8.6.1.1 is applicable to this foundation. The applied vertical force is 100 kips & an applied moment of 295 k-ft. This is an equipment foundation.

Would it be accurate to consider Minimum Flexural Reinforcement ACI 318-19 8.6.1.1 or just insure that the shrinkage & temperature reinforcement requirements are met? The allowable soil bearing is 4 ksf.

Comments/suggestions are appreciated.
 
Replies continue below

Recommended for you

So, there is a flaw (IMO) with the ACI code for minimum slab reinforcement when compared to beams.

When you have reinforcement in a slab, you are required to meet the same flexural minimums that were developed for beams. These insure that there is enough steel to avoid a brittle failure when the beam cracks. However, for beams the code allows you to alternately provide 4/3 of the amount of steel required based on demand moments.

This alternatively is NOT allowed for slabs. So, you have to provide a lot more steel than is necessary (IMO) for thick foundation slabs to resist the loads applied to them.

Also, the Temperature / Shrinkage requirement of 0.0018 must be applied to both the top and bottom layers if they both need reinforcement. Meaning, the total minimum slab reinforcement often becomes 0.0036.
 
My past experience ,
I have provided minimum 0.35 % flexural reinf . ( both ways total ) and additional 0.2 % top and perimeter cage rein. for shrinkage and temp.
 