Regarding underground piping, one gentleman came up with a new idea. The frost depth at site is 3.9 m and he tries to put u/g piping at 2.0 m below surface with 100 mm Styrofoam layer 150mm above the pipes. The Styrofoam should be working as an insulator.
But, I have two concerns.
1)Does it work as insulator to prevent piping from freezing within the frost depth area? In my opinion, the Styrofoam just delays heat transfer between cold surface and piping and at equilibrium state, the service in pipe might be reaching to freezing temperature.
2)Is it durable for life time 20 years? The Styrofoam seems not strong enough to sustain the weight of soil and is going to be squeezed and to lose its insulation effects as time goes.
Could you advise me about this approach, please?