todh
Structural
- May 24, 2005
- 26
A client asked me to look at a building that another engineer designed for him. The building is a pre-engineered metal building with a concrete tilt-up wall panel facade. The typical concrete panels are 25' wide (one bay width) and approximately 25' tall. The panels have embedded (8"x8"x3/8") steel plates with 4 studs embedded in the concrete. These plates are spaced vertically about 6' from the bottom of the panel and 6' from the top of the panel and are used to connect the panels to the pre-engineered metal building rigid frame.
The issue is a crack has appeared during construction at embedded plates welded to the pre-engineered metal building columns. The contractors initial thought was the cold concrete (30-40 degrees when erected) cracked due to the heat caused by welding on the embedded plate.
I do not think this is the cause, but would like a second, third and fourth opinion on the matter to see what others think. The locations of the cracked panels are random throughout the building. They occur in panels with openings and without openings. The attached photo of the worst crack is at an opening for an overhead door. I will attach a close-up in a follow-on post.
At first, it almost appears that the concrete panels shrunk compared to the metal building columns and cracked due to the restrained connection at the columns. The worst case crack happens to be on the first panels poured, so they cured the longest. All panels were erected within 2 days.
Any thoughts? Are repairs required or are the embedded studded anchor rods sufficiently bonded and the crack superficial? The connection just prevents hurricane force (120-mph) winds from pulling the concrete panels off the building. The majority of the cracks appear too small to epoxy inject, however this crack is wide enough to inject.
Thanks in advance for your insight.
The issue is a crack has appeared during construction at embedded plates welded to the pre-engineered metal building columns. The contractors initial thought was the cold concrete (30-40 degrees when erected) cracked due to the heat caused by welding on the embedded plate.
I do not think this is the cause, but would like a second, third and fourth opinion on the matter to see what others think. The locations of the cracked panels are random throughout the building. They occur in panels with openings and without openings. The attached photo of the worst crack is at an opening for an overhead door. I will attach a close-up in a follow-on post.
At first, it almost appears that the concrete panels shrunk compared to the metal building columns and cracked due to the restrained connection at the columns. The worst case crack happens to be on the first panels poured, so they cured the longest. All panels were erected within 2 days.
Any thoughts? Are repairs required or are the embedded studded anchor rods sufficiently bonded and the crack superficial? The connection just prevents hurricane force (120-mph) winds from pulling the concrete panels off the building. The majority of the cracks appear too small to epoxy inject, however this crack is wide enough to inject.
Thanks in advance for your insight.