charliealphabravo
- May 7, 2003
- 796
I have encountered a split in one of the trusses I posted about previously.
I'd like to get some feedback from the forum on the significance of the condition and thoughts about a repair. I have attached a photograph of the split.
On the negative side the split occurs at a split ring connection, is rather wider and deeper that I would expect for a check, and it occurs where the tension load is highest: about 6 Kips total in the (2)3x6 diagonal webs coming up to the connection from the right. I am also concerned that there are no secondary drains on the roof and that the loads could be potentially higher.
On the positive side, the split looks rather old (subjective opinion), only one of the two 3x12 top chords is split, and the bolt passes through the 3x8 compression web which is also not split. According to my preliminary calcs the split rings are good for about 5K each and per the plan there are 6 split rings total at the connection.
I am considering several solutions for a potential repair if I determine that the connection is compromised. The simplest and most direct involves adding a thru-bolt or SDS screws in the tension web above the check. My concern here is that I would be adding some further rotational restraint to the connection.
Thanks all.