Structural
- Mar 16, 2010
- 878
The check for punching shear is correct K1-10. Also check the HSS wall for the weld. Design Guide 24 has a table for minimum wall thickness related to weld size. And as you mentioned the shear plate is designed per 10-101 in the 13th Edition.