Shear Tab/Tube connection? 1

Status
Not open for further replies.

connectegr

Structural
Mar 16, 2010
878
The check for punching shear is correct K1-10. Also check the HSS wall for the weld. Design Guide 24 has a table for minimum wall thickness related to weld size. And as you mentioned the shear plate is designed per 10-101 in the 13th Edition.

 
Replies continue below

Recommended for you

Thanks for the info.

It looks like the HSS shear rupture is going to control the design of the connection (tmin>6.19D/Fu). Therefore, as a general rule of thumb, it appears that you should use 5/16 thick tube as a minumum tube thickness for a tab plate connection (because a 1/4" tab plate requires 3/16 welds).

In this instance a 1/4" tab would require a tmin=0.32017.
 
question is for me, is "D" the required weld size based on strength, or the size actually used based on thickness of material?
 
In 13th Edition the weld size for a single plate is required to develop the plate, but not exceed 5/8(t). The tables in 13th Ed chapter 10 provide weld sizes equal to 5/8(t). To achieve the tabulated capacities, the HSS wall must be adequate for the tabulated weld size.

 
in this case the weld size "D" for a two-sided fillet is 2 x nominal weld size correct?
for example, a quarter inch shear tab weld with a two sided 3/16" fillet would have D=6, correct?

I also dont see where it says that the weld size cannot exceed (5/8)t
 
SteelPE
Another small thought, we rarely calculated shear tabs by determining the minimum plate thickness. Most fabricators prefer to use a standard plate thickness, such as 3/8 bar. Therefore we work the other direction and verify that the wall thickness is sufficient. Most of our projects have columns walls 3/8" or greater, or narrow columns with 5/16 walls. If the minimum wall thickness can not be satisfied per the table above, we provide a "special" case detail.

For a 3/8 plate, K1-10 is satisfied with a 5/16 wall. The b/t ratio is independent of the plate thickness, and 5/16 wall is adequate for 10" columns and less.

 