Erison,
This is a critical issue, please pay attention.
I've evaluated the wall using the following parameters.
- Density of soil = 125 pcf
- At rest pressure coefficient, Ko = 0.5
The resulting shear at the wall base, V = 131 k/per ft of wall, which is far exceeding the concrete shear capacity, Vu Vn = 44 k/ft.
The reason to use at rest pressure coefficient is that it is essentially a propped cantilever beam, for which active earth pressure may not develop. Another things potentially causing problems are ground water, and surcharge at the ground level. I don't think FRP strengthening is able to make up the deficit in strength. Also, I suggest to check the deflection at the top of the wall, which may not satisfy the service criteria.