I'm trying to point someone in the right direction. The issue is that a fire suppression system that discharges a gas into a data center needs pressure relief venting above the 5 psf referenced by the IBC section 1607.15.
We're being asked to calculate the venting requirements at different wall strengths. I'm trying to figure out what wall strengths are common, or listed in a table somewhere, rather than me waiting for them to design a wall. In order to do away with any venting, one of the rooms is going to need a wall strength of 87 psf and I don't think that's realistic. Most of the spaces could do away with venting if the walls could handle 35 psf.
I had looked at "SSMA Product Technical Guide" which references 2015 IBC. The document includes tables for "Combined Axial and Lateral Loads" of 5 to 50 psf (800S200 Stud). These tables list wall heights a 16 feet, which is below the the current wall height of about 25'. They're currently using a 16" spacing, but not sure about the bracing being used.
I'd like to be able to give them their options at the various psf value and reference the studs from the table. For a 800S200 Stud (page 41), with a Mil thickness of 118, and a spacing of 16" is 14.42 the deflection of the stud? [16' / 14.42 = 1.109]?
Am I going about the correctly?
We're being asked to calculate the venting requirements at different wall strengths. I'm trying to figure out what wall strengths are common, or listed in a table somewhere, rather than me waiting for them to design a wall. In order to do away with any venting, one of the rooms is going to need a wall strength of 87 psf and I don't think that's realistic. Most of the spaces could do away with venting if the walls could handle 35 psf.
I had looked at "SSMA Product Technical Guide" which references 2015 IBC. The document includes tables for "Combined Axial and Lateral Loads" of 5 to 50 psf (800S200 Stud). These tables list wall heights a 16 feet, which is below the the current wall height of about 25'. They're currently using a 16" spacing, but not sure about the bracing being used.
I'd like to be able to give them their options at the various psf value and reference the studs from the table. For a 800S200 Stud (page 41), with a Mil thickness of 118, and a spacing of 16" is 14.42 the deflection of the stud? [16' / 14.42 = 1.109]?
Am I going about the correctly?