Diagram attached. I've done a bunch of reading on parallel pumping. I've run the two main pumps independently (both off, one on, other on, both on) and got some pressure readings. My question stems from finding a TDH needed for the third pump. It's entirely different in flow, head requirements, operating time, pump style, etc. The flow is an order of magnitude lower than the #1 Sump system and is very intermittent (few times a day for one or two minutes) as opposed to the relatively constant flow of the #1 Sump. If the pressure gauge is reading 25 psig before a vertical rise, can I assume the pressure at the tie-point located at the top of the rise is 25 psig - 5psig = 20 psig? The system discharge is unknown as it is a pipeline that goes offsite to a treatment plant but it does run underground before leaving our property. I just need to make sure I can empty the #2 Sump into the header regardless of what the #1 Sump is doing. The volume of #2 Sump is low enough that if the #1 Sump isn't running, we won't have enough liquid to make a difference in the larger pipe of the header so we don't have to worry about pumping this stuff all the way to the treatment plant.
I've done some modeling in EPAnet as well and those results don't closely match my Excel numbers but I don't know that I trust EPAnet as it may be a case of garbage in, garbage out. This is my first foray into adding a downstream pump to a force main.
The piping and infrastructure already exists, I'm trying to shoehorn a pump into the system that will work without any serious piping overhaul as it's all either in the air or underground.