From my Project Notes:
CONCRETE QC
WATER SHALL NOT BE ADDED TO THE CONCRETE MIX ON SITE UNLESS APPD IN WRITING BY THE CONCRETE SUPPLIER AND AUTHORISED BY THE ENGINEER
PROVIDE HISTORY OF CONCRETE MIX USE IN ACCORDANCE WITH CSA A23.1
TESTING SHALL BE IN ACCORDANCE WITH THE REQUIREMENTS OF CSA A23.1 UNLESS NOTED OTHERWISE
A MINIMUM OF THREE CYLINDERS SHALL BE TAKEN FOR STRENGTH TESTS, ONE CYLINDER FOR 7 DAY STRENGTH AND TWO CYLINDERS FOR 28 DAY STRENGTH
TEST CYLINDERS SHALL BE 6" DIA X 12" HIGH U/N
SLUMP TESTS SHALL BE TAKEN WITH EACH SET OF CYLINDERS TAKEN FOR STRENGTH TESTING
AIR CONTENT TESTS SHALL BE TAKEN FROM EACH LOAD UNLESS A REDUCED FREQUENCY IS AUTHORISED IN WRITING BY THE [OWNER | CONSULTANT | ENGINEER]
CYLINDERS FOR STRENGTH TESTS AND A SLUMP TEST SHALL BE TAKEN FROM AT LEAST EACH THIRD TRUCK
A MINIMUM OF THREE CYLINDERS FOR STRENGTH TESTS, AND A SLUMP TEST SHALL BE TAKEN EACH DAY FOR EACH DIFFERENT TYPE OF CONCRETE MIX DESIGN
WHERE THE FREQUENCY OF TESTING ABOVE WILL PRODUCE LESS THAN THREE TESTS FOR A GIVEN CLASS OF CONC, TESTS SHALL BE MADE FROM AT LEAST THREE RANDOMLY SELECTED BATCHES
IF LARGE VOLUMES OF CONCRETE ARE BEING SUPPLIED (OTHER THAN BY TRUCK), THERE SHOULD BE A MINIMUM OF THREE CYLINDERS TAKEN FOR STRENGTH TESTING, ONE AIR TEST AND ONE SLUMP TEST FOR EACH 100 CUBIC METRES OR PART THEREOF
CARE SHALL BE EXERCISED IN PROTECTING THE TEST CYLINDERS FROM DAMAGE
TEST CYLINGERS SHALL BE PROPERY CURED
IF TEST RESULTS SHOW A LARGE 'SCATTER' OF DATA, ADDITIONAL TESTING SHOULD BE PRESCRIBED
THE TESTING AGENCY SHALL FORWARD A COPY OF ALL TEST RESULTS DIRECTLY TO THE [OWNER | CONSULTANT | ENGINEER] AT THE TIME THE TEST RESULTS ARE FORWARDED TO THE CONTRACTOR
IF CONCRETE SPECIFIED IS IN EXCESS OF 35 MPA, THE CLIENT SHALL ARRANGE FOR THE GEOTECHNICAL CONSULTANT TO REVIEW THE CONCRETE BATCH PLANT
FOR TESTING MASONRY GROUT, REFER TO NOTES ON MASONRY CONSTRUCTION
Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better?
-Dik