JP said:
1) I don't believe the OP never said that his footing was cracked. Only that the positive moment would exceed Mcr. You're assuming that it will eventually crack. That's a reasonable assumption. But, I don't know that this really negates the use of these design provisions.
I'm pretty sure that OP is concerned about a cracked footing. And, clearly, whether or not cracking invalidates the plain concrete provisions is the crux of this debate.
OP said:
Does not plain concrete design require everything remain uncracked for all loading conditions?
JP said:
2) If the top of the footing is essentially uncracked until the ultimate design load is reached, then you're not trying to transfer tensile stresses across a crack. Maybe you have limited cracking at the bottom of the footing if you've gone through a design level event in the other direction. But, that's on the compression side of the footing for the negative bending load case. And, the level of cracking has been limited by the presence of the reinforcement.
This essentially amounts to my proposed, but not recommended, design strategy #1 above. Additional thoughts:
a)I find it hard to imagine that any engineer would want life safety hinging on their ability to estimate the depth of flexural tension crack accurately.
b) If a footing's ULS uplift capacity is dependent upon that footing never having previously reached ULS gravity capacity, I would definitely question the soundness of the design strategy.
c) To use the full section in plain concrete flexure post-cracking, you'd need to ensure that the cracking didn't extend past mid-depth. Even early in the loading history, there's pretty good chance that a member will see cracks penetrating deeper than that.
d) A small crack is no better at transferring tensile stress than a large crack is.
JP said:
3) Commentary says, "Use of structural plain concrete should be limited to members that are primarily in a state of compression, members that can tolerate random cracks without detriment to their structural integrity, and members where ductlility is not an essential feature of the design."
How are we to know that members able to tolerate cracks aren't just members loaded primarily in compression? Or members not requiring water tightness? I get what you're pointing to here but, for me, it would take a far more definitive statement of intent before I'd be willing to conclude that chapter 22, which mentions concrete modulus of rupture every other paragraph, applies to cross sections already cracked in tension.
JP said:
4) This type of footing does not have the type of "restraint" from creep, shrinkage or temperature effects that are generally of a concern. Right? The top face of an individual spread footing is essentially unrestrained. This seems to be exactly the type of situation ACI is talking about for this chapter.
I disagree. A large, heavily loaded footing on sedimentary bedrock will experience restraint at the bottom due friction with the bearing surface. And the top of the footing will be similarly restrained by it's horizontal shear connection to the bottom of the footing. Chapter 22 clearly is meant to apply, at least, to footings that are uncracked. Chapter 22 also makes much of considering creep, shrinkage, etc for plain concrete members. And they make no mention of excluding footings from such consideration. As I mentioned above, I'm really not sure if footings are meant to be excluded from such scrutiny. I've never personally known anyone to consider it in design.
JP said:
5) When the commentary says that the shear requirements assume an uncracked section, they are talking about the stress model used to derive the equation. v = VQ/Ib and the dimensions used to calculate these values. They also talk about how this will rarely control the design of a plain concrete member.
I disagree. The statement made is simply that "the shear requirements for plain concrete assume an uncracked section". To me, the fact that the VQ/Ib method also assumes an uncracked section only reinforces the notion that chapter 22 shear capacity is intended for uncracked concrete. And, if a cracked section means zero shear capacity, then you can bet that it
will govern.
I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.