Masonry Wall Construction

SteelPE

Structural
Joined
Mar 9, 2006
Messages
2,773
Location
US
I have a project that a client is asking me to prepare a proposal for. The building is a single-story building in an area with a wind speed of 131 mph. The building is anticipated to have an eave height of 20'-0" with dimensions of 146'x68' and utilize open-web steel joists and masonry bearing walls. The project is pretty straight forward with the exception that the client is looking to use 8" CMU.

Our company standards have us moving away from 8" CMU around 16'-0" to 18'-0". There is no real reason for our limit other than this is what has historically worked for us (other than the old h/t limit of 30 outlined in ACI 530 which limits 8" CMU to 20'-0" before you have to take a 75% reduction in axial capacity for the bearing wall). For this project we are trying to figure out a way to get the clients system to work before we put in a proposal. We are considering using the depth of the roof joists system (24" deep roof joists) and support the walls off the bottom chord of the joist. This would require a system of kickers and bridging in order to properly transfer this force up o the roof diaphragm. It's an unorthodox solution for us. Has anyone attempted to brace masonry walls in this manner before?

To me, as long as we can transfer the loads to the diaphragm properly, I don't see why it wouldn't work. Would it be cheaper than switching to 12" CMU.... unfortunately that is above my head.
 
Can you not get enough rebar in the wall to make 20 feet work? The diagonal bracing seems reasonable as well.
 
I worked on a local shopping center that had 20 ft, 8" CMU walls. They were not even fastened to the edge angle. The only thing bracing them was the 25 ft. O.C. I-beams. Wasn't a known issue until there was significant unrelated foundation settlement that caused the wall to start leaning outwards.
 
I've done exactly what you have proposed with a 32" deep joist.

You could also coordinate w/ joist mfg and just tie the bottom chord to the anchors.

I used angle kickers to embed pl, then they come up to a perpendicular angle that is supported by the roof joists.
 
Can you not get enough rebar in the wall to make 20 feet work? The diagonal bracing seems reasonable as well.
I am not sure what we will be able to do as we are just trying to put together a scope of fees for the client and are investigating the feasibility of what the client is proposing. I am not sure where you are located (I can look that up after I type out this response) but 131 mph wind speed isn't anything to shake a stick at.

I've done exactly what you have proposed with a 32" deep joist.

You could also coordinate w/ joist mfg and just tie the bottom chord to the anchors.

I used angle kickers to embed pl, then they come up to a perpendicular angle that is supported by the roof joists.
I understand the coordination part. Going to require a bunch of effort there..... however, what you propose (attaching the bottom chord of the joist to the masonry wall) I would be nervous this would create a moment in the joist which would cause other issues. I have thought about possibly using a square end joist, but I am not sure if I can get that to work or not without inducing moment in the end of the joist.
 
.....create a moment in the joist which would cause other issues. I have thought about possibly using a square end joist, but I am not sure if I can get that to work or not without inducing moment in the end of the joist.

Its unconventional but I'm told the joist MFG can account for this. But I had the same thought as you and opted to keep it conventional as possible.
 
Its unconventional but I'm told the joist MFG can account for this. But I had the same thought as you and opted to keep it conventional as possible.
They can account for this, but the real question is WILL they account for it?

Personally I would push for 12" block, or even 10". Will be a lot less grouting and smaller bars. Remember that lift heights for the grout can become an issue with larger bars and lap lengths.
 
I have a project that a client is asking me to prepare a proposal for. The building is a single-story building in an area with a wind speed of 131 mph. The building is anticipated to have an eave height of 20'-0" with dimensions of 146'x68' and utilize open-web steel joists and masonry bearing walls. The project is pretty straight forward with the exception that the client is looking to use 8" CMU.

Our company standards have us moving away from 8" CMU around 16'-0" to 18'-0". There is no real reason for our limit other than this is what has historically worked for us (other than the old h/t limit of 30 outlined in ACI 530 which limits 8" CMU to 20'-0" before you have to take a 75% reduction in axial capacity for the bearing wall). For this project we are trying to figure out a way to get the clients system to work before we put in a proposal. We are considering using the depth of the roof joists system (24" deep roof joists) and support the walls off the bottom chord of the joist. This would require a system of kickers and bridging in order to properly transfer this force up o the roof diaphragm. It's an unorthodox solution for us. Has anyone attempted to brace masonry walls in this manner before?

To me, as long as we can transfer the loads to the diaphragm properly, I don't see why it wouldn't work. Would it be cheaper than switching to 12" CMU.... unfortunately that is above my head.
You should look at slender walls if you haven't already. That approach eliminates the h/30 issue.
 
Send in two proposals, one for 8” CMU, one for 12” CMU. Make the former 10x cost of the latter.
 