EEiAM
Electrical
- Aug 17, 2008
- 2
I am working on a project to add kW/kVAR transducers to an existing 3-phase system. There is a 13.8kV-138kV step-up transformer in this section of bus. The 13.8kV side is grounded wye and the 138kV side is configured as an open delta. All of the current transformers (C/Ts) on the 13.8kV side are being used for protective relaying. The C/Ts on the 138kV side are spare. The only potential transformer (P/T) in this section of bus is on the 13.8kV section. An easy solution would be to feed the kW/KVAR transducers with the P/T on the low side (13.8kV) of the xfmr and the C/Ts on the high side (138kV) of the xfmr. My concern is the 30 degree phase shift in voltage and current due to the wye-delta transformation.
Is there any way to compensate the circuit for this phase shift so that the kW and kVAR readings are accurate with the setup described above? Would arranging the three C/Ts on the high side of the step-up transformer in a wye configuration offset the phase shift in current (since the step-up transformer high-side windings are delta)?
Any advice or recommendations are appreciated. Thanks.
Is there any way to compensate the circuit for this phase shift so that the kW and kVAR readings are accurate with the setup described above? Would arranging the three C/Ts on the high side of the step-up transformer in a wye configuration offset the phase shift in current (since the step-up transformer high-side windings are delta)?
Any advice or recommendations are appreciated. Thanks.