Dec 3, 2004 #1 2766ast Industrial Joined Dec 3, 2004 Messages 1 Location US I am trying to comfirm the kW useage of a 3 phase system. Each leg is 280 volts drawing 1300 amps. Volts = 1.732 * 280 =485 P = (1.732 * 485 * 1300 *.9)1000 = 982.8 kW Is this correct?
I am trying to comfirm the kW useage of a 3 phase system. Each leg is 280 volts drawing 1300 amps. Volts = 1.732 * 280 =485 P = (1.732 * 485 * 1300 *.9)1000 = 982.8 kW Is this correct?
Dec 3, 2004 1 #2 aolalde Electrical Joined Dec 16, 2003 Messages 1,022 Location US If your Power Factor is 0.9 and the "leg voltage" is line to neutral voltage, your calculation is correct. Upvote 0 Downvote
If your Power Factor is 0.9 and the "leg voltage" is line to neutral voltage, your calculation is correct.
Dec 3, 2004 1 #3 tinfoil Electrical Joined Jun 24, 2004 Messages 351 Location CA Another way of expressing that is that each phase is using p.f. * Current * Voltage (L-N), so (if current is balanced) three phases are using: Power(W)= 3 * p.f. * Current * Voltage (L-N) Power(VA)= 3 * Current * Voltage (L-N) Upvote 0 Downvote
Another way of expressing that is that each phase is using p.f. * Current * Voltage (L-N), so (if current is balanced) three phases are using: Power(W)= 3 * p.f. * Current * Voltage (L-N) Power(VA)= 3 * Current * Voltage (L-N)
Dec 4, 2004 #4 advidana Electrical Joined Dec 24, 2002 Messages 433 Location US yes Upvote 0 Downvote