Injection System spacing

Status
Not open for further replies.

Catlin987987

Mechanical
Joined
Jan 21, 2009
Messages
1
In an injection system what is the typical spacing on the supply and return compared too pipe size.

download.aspx
 
Can anyone give me info on how injection/rejection works?
 
I don't know that there is any typical spacing versus pipe diameter.

...which may be the reason that no one else has answered as well.

Patricia Lougheed

Please see FAQ731-376: Eng-Tips.com Forum Policies for tips on how to make the best use of the Eng-Tips Forums.
 
Maximum spacing between the tees should be less than 4x the pipe diameter of the primary pipe in order to minimize the pressure drop between the supply and return tees. You want to minimize the pressure drop to hydraulically separate the injection pump system from the primary system.

John Siegenthaler has some great articles on hydronic system design.
 