Many architectural assemblies we see refer to the Gypsum Association (G.A.) Fire Resistance Design Manual. Early on in this manual, there is a note regarding reduction of compressive strength values. It is similar to footnote "m" in the IBC fire-rated assemblies table in Chapter 7. Basically, if the fire-rated assembly is from the G.A. manual or is in the IBC table and has this footnote, then the F'c parallel value has to be reduced by a factor of 0.78 when designing wall studs. This is straightforward, but the part about slenderness ratio makes me nervous. (The excerpt from the G.A. Manual 2009 is below in quotes). If I have a 2x6 wall stud and it's 9' tall, then I have to assume that it's more than 15' tall (for l/d = 33 minimum) in order to calculate a Cp factor and then adjust my Fc parallel to obtain my allowable design value. For a 2x4 wall, I would have to assume 9'6" tall studs, which is not as bad, but it still needs to be checked for most of the platform-framed walls I design.
I'm getting ridiculous stud spacing for 2x6 corridor and demising walls on a 3-story building with #2 Hem Fir studs [(2) 2x6 @ 12" o.c. not working] and it's all being controlled by the low compression parallel to grain design values when checking the wall stud stability. Do others here agree with how I interpret these limitations and how have you handled this? I'm thinking that I need to have a conversation with each architect about which assemblies they should avoid, but that feels like stepping on the client's toes to me and I'd rather not, if possible.
"Unless indicated otherwise, all load-bearing wood
stud systems were tested while being subjected to the
maximum load allowed by design under nationally
recognized design criteria at the time of the test. Due to
an increase in the maximum allowable loading in the
National Design Specifications (1982 and later editions),
the American Forest and Paper Association issued the
following statement:
Where a load-bearing fire rated wood stud wall
assembly contained in this Manual is specifically
designed for structural capacity, the design value in
compression parallel to grain adjusted for slenderness
ratio (Fc') used in such analysis shall be taken as 78
percent of the maximum Fc' value determined in
accordance with normal design practice but shall not
exceed 78 percent of the Fc' value for such member."