Im looking for the calculation for finding gpm thru a plate heat exchanger for a 30 ton chiller
 
Q=m*C*(T1-T2)?

You must be able to tell us more than that.
 
There are a lot of basic design parameters that you have to specify, i.e., what is the design delta T for the coolant, what is the design ambient?

As an example, based on a system we designed for a smaller military application with a 5°C delta T and 400 W load, the scaled coolant flow would be 264 gpm, but that probably has little correlation with your system

TTFN

FAQ731-376
 
Call the manufacturer with the pressure drops across it. He'll be able to tell you within a few minutes exactly what the flow is.
 