Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

gpm thru plate heat exchanger

Status
Not open for further replies.

thelobster

Mechanical
Apr 26, 2005
9
Im looking for the calculation for finding gpm thru a plate heat exchanger for a 30 ton chiller
 
Replies continue below

Recommended for you

Q=m*C*(T1-T2)?

You must be able to tell us more than that.
 
There are a lot of basic design parameters that you have to specify, i.e., what is the design delta T for the coolant, what is the design ambient?

As an example, based on a system we designed for a smaller military application with a 5°C delta T and 400 W load, the scaled coolant flow would be 264 gpm, but that probably has little correlation with your system

TTFN

FAQ731-376
 
Call the manufacturer with the pressure drops across it. He'll be able to tell you within a few minutes exactly what the flow is.
 