Existing PEMB - Multi Column Removal/Jack Truss
BuildWithSteel
1
Modifying PEMB- am interested to hear what solutions others might have gone with in my situation, even if I end up regretting the final solution I landed on.
Multispan, existing pre-engineered metal building- 4 bays, 54’ wide, PEMB bents at 25’ on center- total building length about 350’ long. Interior columns are Pipe 8”- couldn’t say for certain wall thickness at time of design other than tapping the column to hear the tone of “ping” it made- it sounded thin LOL. I wouldn’t have actually trusted that “test” if I had actually planned on somehow attaching to existing columns. Exterior columns are typical built up tapered plate columns.
Assumed interior columns are pinned top and bottom for only gravity based off of light, simple beam over column cap plate connections and base plate configuration- bolts from cap plate to PEMB bent was only 1/2” diameter as an example.
I needed to remove 2 of the interior ridge line columns for a 75’ clear span.
Attached photos was my solution- reinforced/enlarged the existing footings each end, 2-new pairs of columns added each end, sandwiched existing column line with a trusses braced to eachother each side as a jack beam/truss, existing columns cut out once all connections made- no shoring was needed this route. It’s not a fancy solution- one that you can look at and logically see exactly how it works. Possibly a bit overdone.
What might have you done differently in situation?
Actually looks simple and reasonably conservative to me. I do not know how much wind load you have where you are at, but I assume you checked the truss for LTB of the lower chord for wind uplift. I did not see any lower chord lateral braces at the frame lines but not needed if the lower chords can span 75' with no lateral bracing. I assume your top chord unbraced length is 25'
Also it does look reasonable to assume the interior columns are pin-pin. Most PEMBs are designed that way even though there are no guarantees and your baseplates and top plates look like pinned.
Is this a new approach to a "humble brag"? Post something clever you have done and ask others how they would have done it differently? ( :LOL: joking)
I agree with Ron. This seems like a good solution. The best choice here IMO was to design an approach that didn't need shoring. That makes life signifcantly easier for the guys on site. And saves money even if you end up with more steel than a non shored outcome.
The truss seems to be on the heavy side. But maybe you needed that for the deflection or LTB. LTB could have been restrained by the rafters (fly braces for uplift) but that would start making things more complicated. You seemed to have adopted, clever, simple but not necessary weight efficient. But sometimes that is the best approach.
If I was designing that truss I likely wouldn't have back to back angles. You are increasing the welding significantly and likely making painting harder. I would have chosen H-sections for my cord and angle or HSS for the web member depending on loads.
But that is just my initial thoughts and comments there are many was to skin this cat. Your way seems very effective.
Very nicely done. I'm a PEMB guy. The 8" pipe columns are schedule 40 std 8" pipe. Round HSS is not readily available on the market despite being listed in the steel manual. also the pipe column was definitely designed as pinned-pinned.
I jacked out a column supporting (2) 5 ton cranes on either side. Designed it for the loads and held a very stringent deflection. They installed the beam and then cut the column and started letting it down. It should have only gone down 3/8" even with crane loads but it went down further. I had them stop and weld the top of the column back up to the top. Ended up reinforcing my beam to be many times stiffer than what my numbers said it should be and that has worked great. Long story short, no reason to get cute with this type of thing. If you think your solution is a bit overdesigned, it may not be.
The stiffness of the truss and columns may attract some lateral load to the interior of the building and away from the cable or rod braces at each end. I would analyze whatever stiffness it has and make sure the strut purlins in the area can take any redistributed loads. You may have done this.
I've been meaning to post the same thing for a while. Though the rod bracing isn't really relevant unless we are talking different directions.
Portal frames of this size can often move 100mm+ in the direction of the portal framing in ultimate cases. The previous columns were pinned top and bottom and would sway with the building. This setup is mostly a rigid connection to the footing.
Though I notice you have forgone a final diagonal to the ground. Maybe you did this for this very reason and this allows enough flex in the channels. That is certainly my approach.
I want to add something about the flexibility of PEMB structures--They're much more rigid than you think in the direction perpendicular to the rigid frames due to an abundance of redundancy. Hypothetically, wind load travels from the top of wind columns through strut purlins until it hits the diagonal bracing, then the diagonal braces, rafters and additional strut purlins form a truss to provide a load path to the ground. These are always designed by PEMB manufacturers as idealized trusses with all connections pinned.
In reality, in order for the building to move in that direction, every purlin would have to move in that direction and each of them provides a small moment resistance to that movement. Where flange braces are provided you have even more resistance to that movement. This redundancy is not taken into account in their design.
Next the diaphragm capacity of the roof sheeting is neglected but still exists. Even for PEMB structures with deck roofs, that capacity is ignored and x-bracing will be provided.
There are plenty of reasons to hate PEMBs, as this sub reminds me every few months. This just isn't one of those areas.
All this is to say, that I wouldn't worry too much about load from the roof bracing system getting into this truss support. Also, how would you calculate the true stiffness of the PEMB system? We can't even calculate it.
The wall rod bracing is about 2 bays past the portal. The rods look loose in the picture. If they are, I would snug the roof and wall rods to minimize lateral movement before the rods tighten from the movement. If the wall panels are capable of diaphragm action, they are probably what are doing the work at the sidewall anyway
I want to add something about the flexibility of PEMB structures--They're much more rigid than you think in the direction perpendicular to the rigid frames....
Except that is not the direction I was referring to. It should be obvious to any moderately experienced structural engineer that these structures are significantly stiffer the cross portal direction as these are braced compared to the portal direction as these rely on moment frames.
Of course end bay sheeting and roof sheeting might provide a decent degree of stiffness that isn't considered, but I wouldn't rely on that at high service conditions or ultimate conditions.
Or the purlins could just buckle. Which is quite possible as their compression capacity is very low. I've seen what happens when this isn't considered. The following photo shows purlin buckling that occurred during a severe storm. Further damage was likely averted as when the wall on the right moved the roller door came off its tracks and relieved the some of the wind load. Cracking was observed around the footings of the wall mullions indicating that they had rotated somewhat during the event.
Yeah I noticed that too. But as you commented with that wall the rods likely served their purpose better as safety during errection than anything else.
The comment I was responding to was the one above yours which is about the loading in the direction perpendicular to the rigid frames, in particular if the above fix would suck some load from the bracing system which has nothing to do with the lateral system of the rigid frames. Any experienced structural engineer could see that.
And the example of purlins buckling if they aren't designed properly has nothing do to with my comment. Any type of system can fail if not designed properly. Work with reputable people companies.
Do those buckled purlins have any purlin bracing? The bay does not look very wide, but the purlin also does not look very deep.
I now see what I think are the rods in the roof a couple of bays down. I've also seen these buildings with what looked like 1/4" or 1/2" diameter cables that weren't tight. For assuming it is like a rigid diaphragm in that direction, I wouldn't personally do that without checking the purlins for some load assuming it goes directly into the new portal frame, especially with these cables or rods often not being installed correctly, at least in my area. If it were those slack wire cables, then I would be even less likely to assume it behaves initially as a rigid truss. But I understand the assumptions behind their design. I don't know any of the sizes of the new tube columns or connections to the footings so perhaps the new frame isn't as robust as it looked to me. For loads in the main building rigid frame direction, yes that obviously also creates a stiff point.
I don't design metal buildings, but we are more cautious of them in general. When we give the spec criteria for allowable drift, we give a more strict requirement and don't leave it up to the mfr. Unfortunately, most everyone I know considers them as cheap junk. Maybe that is why I wouldn't automatically assume anything with one.
One thing I've noticed is that purlin design has changed a lot in the last 20 to 30 years. I look at buildings that were built in the 90s, and the purlins are spanning 25' with zero bracing. The same design now has third point bracing. So on "older" designs it's important to be aware of this. New designs should be more resilient.
You guys are correct. The strut forces in the purlins used to be neglected in design. I heard that from an old timer when I started 20 years ago. Hasn't been that way since I started. You don't necessarily need purlin bracing if you have a through fastened roof because the AISI has formulas for calculating a torsional brace to the inside flange based on the stiffness of the through fastened panels. These days, almost all roofs are standing seam with clips that allow the roof to slide compared to the purlins for thermal expansion. You can do testing on your specific system to see how much rotational restraint it provides but usually, they're assumed to not brace the top or bottom flange so you need some kind of flange restraint at third or quarter points.