Hello folks,

How would you go about estimating how far away a cable rated for 90 C has to be from a stack?
This cable is a 4-20 mA signal from a temperature transmitter installed on the stack itself.

I thought I would estimate the thermal radiation from the stack using AERflare spreadhseet (Publicly available).

Then add on top of that (worst case scenario):
- Radiation from sun, convection with worse wind blowing hot air from the stack to the cable, neglect any conduction and somehow come up with a worse case temperature.

What do you guys think? I'm just curious how you would approach this!?

 
how hot is the stack?
what is its emissivity, since that's the most likely thermal load?
Can you wrap the cable with metal or reflective film?

TTFN (ta ta for now)
I can do absolutely anything. I'm an expert! faq731-376 forum1529 Entire Forum list
 
I would treat it the same as a fireplace chimney. Bldg. codes dictate how high about the roof and how far away (horizontally) the muzzle of the stack must be from a flammable surface and add your choice of a safety factor.
 
@trashcanman : That's a good idea. I'll look up the code, Thanks!

@IRstuff : I have stack temp and emissivity. But then I'm stuck at what equation to use.
If I need to use a radiative view factor I'm using the "From small hemisphere to a large sphere).
But the result I get for the cable temperature doesnt make sense. I must be missing something.

I'm isolating T1 based on the equation below. Since I know the heat flux q(2=>1)(W/m^2)from the stack, I just assumed Q(2=>1)/A1 = q(2=>1)
Q(2=>1) = A1 x F(1=>2) x sigma x (T2^4 - T1^4) x Epsilon2

With:

Q(2=>1) = Heat transfer rate (W) from surface 1 to surface 2
q(2=>1) = heat flux (W/m^2)
A1 = Surface 1 (m2)
F(1=>2) = View factor from surface 1 to surface 2 (Using 0.5*(1-SQRT(1-1/h^2)+1/2*h^2)) with h = H/R with H = 1m and R=0.305m = 2.71
sigma: Boltzmann constant = 5.67e-8
T2 = Temperature of surface 2 = Assumed to be around 480 (K)
T1 = Temp of surface 1

epsilon2 = emissivity of surface 2 = 0.3 (Not sure - its a steel stack)

Surface 1 = Cable
Surface 2 = Stack

Writing equations is painful here, any tips for that?
I'm attaching my spreadsheet for the braves lol. Easier than typing all that stuff.
 
 Cable_Temp_Approximation.xlsx
Did you not read anything about the equation you chose? You essentially placed the cable almost next to the stack. Your spreadsheet link doesn't work

TTFN (ta ta for now)
I can do absolutely anything. I'm an expert! faq731-376 forum1529 Entire Forum list
 
Hi,
Could you use an infrared camera or pyrometer to check at the wall along the stack? This will give you more confidence than calculation?
My 2 cents
Pierre
 
Thanks guys, good idea @pierreick
I'll check this @IRstuff, thanks!
 
All of this focus on the cable but what about the 4-20mA signal amplifier? Those also have temperature limits. I would consider using a thermocouple and running a high temperature extension cable rated for your worst case scenario. Convert to 4-20mA in a location that isn't as harsh.
 