Take a look at this, Cuky;
I found a paper that does an excellent job of explaining all aspects of 6 phase transmission and touches on 12 phase transmission as well. Only 79 pages.
A must read for anyone interested in High Phase Order Transmission.
I noted this quote:
"As a result, there has been a generation of a plethora of information which is very beneficial on the one
hand, but on the other is sometimes contradictory and inconclusive. Thus, there is a formidable challenge
in compiling a survey of case studies, and careful thought must be given to the selection of cases and their
applicability."
Link
Transmission Line Compaction Using High Phase Order Transmission
Jacob Bortnik
A dissertation submitted to the Faculty of Engineering, University of the Witwatersrand, Johannesburg, in fulfillment of the requirements for the degree of Master of Science in Engineering Degree awarded with distinction on 8 December, I998
Johannesburg,1998
Mr. Bortnik examines and comments on six case studies of High Phase Order Transmission Lines.
Here are all the answers that I couldn't find in the other paper.
Some take-aways;
HPO, Less inductive reactance per unit length, less need for series capacitors.
HPO, Comparable construction costs to equivalent 3 Phase lines.
The breakeven point may be under 15 km, however some configurations never reach a breakeven point
HPO, Generally less corona, less radio noise, less audible noise, lower electric and magnetic field strengths at a given distance from the line.
3 phase; Where same voltage systems are connected by a transmission line without transformers, the HPO option may never be feasible.
The future;
The main advantages of HPO will develop in the future with rising land costs for ROW, restricted ROW, and restriction on the radiation of electrical and magnetic field gradients.
A couple of notes on the previous discussion;
Using an averaging voltmeter on unloaded wye transformer circuits? I have been bit by that one a couple of times.
Well balanced, and the ability to operate with one phase missing. The receiving end is a pair of grounded wye-delta transformers.
That's what they do.
The ability to run with a missing phase and forcing balance on an unbalanced system?
They do that by way of creating zero sequence current on the neutral.
Those effects are grounded wye-delta effects, not HPO effects.
I fought the good fight with the ideosyncrasies of the grounded wye-delta for over 15 years.
Total costs as opposed to line construction costs;
Two winding transformers needed, cheaper auto-transformers are not suitable.
The addition of extra substation costs may push the breakeven point out to 200 to 250 km.
I anticipate bulk transmission from distant generating system by HVDC, and possibly HPO from HVDC terminals into cities on ROWs subject to high land cost and stringent environmental regulations.