Cuky, your graph shows the thermally limited power density as proportional to the number of phases.
eg: The thermally limited power density for six phases is twice the thermally limited power density of three phases.
Six conductors is carries twice as much as 3 conductors or 200%.
But the surge impedance limit is only 173%
Not quite as good as two three phase circuits.
They converted two circuits and got 173% of the capacity of one three phase circuit.
200% as much conductor and more expensive towers for a 173% gain?
I admit that there may be an advantage in restricted right of ways, but why use special expensive towers for a 173% gain when you can use twin circuit towers for a 200% gain?
I admit that there may be lower impedance when the conductors are in a hexagonal arrangement but that will be offset by the added impedance of the delta wye transformers.
In a relatively short time the industry gained a 173% advantage by changing from delta to wye distribution.
Now I am told that industry is turning their back on another 173% gain?
I saw a note that I can't find again. It seemed to indicate that this project was a pilot project for a planned 400 kV line.
The 400 kV six phase line was never built.
I have spent several hours searching for any information as to whether the original circuits were delta or wye.
Can anyone help with this?
Corona: one part of the information claims less corona with six phase.
In another place it indicates that the voltage was lowered because of corona concerns.
I repeat (with a slight edit)
Energized in 1992, de-energized in 1995. Never done again. That says it all.
You just spent over $10 million and did not get the dramatic results that you hoped for.
Now write the report and try to make yourself look as good as you can.
Bill
--------------------
"Why not the best?"
Jimmy Carter