Convert two deltas to wye and reverse the polarity of one circuit and you have six phases.
The delta system would be insulated for 115 kV to ground and the voltage to ground would remain at 115 kV.
Six phase is touted as reducing corona but one note indicates that the voltage was reduced because of corona concerns.
That will cut into the +73%.
Oh well. I read it on the internet.
You will get the 73% increase or 173% of original capacity (depending on how you phrase it) that a conversion from delta to wye provides. That holds for three phase or six phase.
Takeaways from the summary of the 493 page report, Reference 3 in the Wiki article linked by Bill West.
Page 22,
Will it work? Yes
Did it work? Yes.
Is it worth converting existing double circuits? Probably not.
Is a single tower, compacted conductor scheme cost effective? No, but it may have applications on restricted Right Of Ways.
Why was it de-commissioned? The transformers were limiting the capacity of the line.
There may be special constraints on both the maximum voltage and ROW restriction.
In that case it may be a choice to go with a six phase system.
Normally, one would just choose a higher voltage for the required capacity on a new build.
Energized in 1992, de-energized in 1995. That says it all.
That internet article badly needs editing.
Wiki said:
Compared to a single-phase, two-wire system, a three-phase three-wire system transmits three times as much power for the same conductor size and voltage.
Also;
The author seems to think that adding more poles to an induction generator implies higher phase orders.