Engi-Peers,
I'm designing a narrow building with a concrete core in the middle which will serve as the building's sole lateral system (see attached sketch). Originally, we had proposed framing the floors with beams and two-way slabs. In a effort to economize, we're considering using a 12", one-way composite deck system instead. Surprisingly, this system appears to be capable of spanning the entire short dimension of the building (9 m). My concerns are twofold:
1) Where the one way concrete abuts the core walls and runs parallel to them, there will be a differential deflection between the floor system and the walls of 1.5" (L/240) and;
2) Behind the core walls, there will be a shorter one-way spanning floor system. Differential deflection between the long span and short span floor systems will be about 1" where they abut.
How should one deal with this differential deflection? Can it be detailed away somehow? Can it be shown to be adequate by calculation? Am I over thinking this?
It seems to me that these problems must have already been resolved in the past for both precast hollow core and one-way pan-joist systems. While I couldn't find any relevant details or discussion for pan-joists, I found plenty for hollow core slab systems. Unfortunately, if the precast details addressed these issues at all, they did so only for initial dead load deflections (camber), not for live load or long term deflections.
With regard to this issue, PCI's Manual for the Design of Hollow Core Slabs says:
The effect of different vertical stiffnesses may be accounted for by:
1. Determining that distress will not affect the strength or performance of the system,
2. Locating vertically rigid connections near the slab supports where vertical movement is minimized, or
3. Providing allowance for vertical movement in the connection detail.
How have others been dealing with this? Part of my concern is that the "joist" members are closely spaced and no one joist is capable of supporting all that much load. If I say that the topping slab is able to span perpendicularly to the joists for a distance that justifies allowing the joists to "hang up" against the wall, that topping slab will be spanning to a joist member that likely cannot support the additional tributary load.
Thanks for your help.
Kootenay Kid
I'm designing a narrow building with a concrete core in the middle which will serve as the building's sole lateral system (see attached sketch). Originally, we had proposed framing the floors with beams and two-way slabs. In a effort to economize, we're considering using a 12", one-way composite deck system instead. Surprisingly, this system appears to be capable of spanning the entire short dimension of the building (9 m). My concerns are twofold:
1) Where the one way concrete abuts the core walls and runs parallel to them, there will be a differential deflection between the floor system and the walls of 1.5" (L/240) and;
2) Behind the core walls, there will be a shorter one-way spanning floor system. Differential deflection between the long span and short span floor systems will be about 1" where they abut.
How should one deal with this differential deflection? Can it be detailed away somehow? Can it be shown to be adequate by calculation? Am I over thinking this?
It seems to me that these problems must have already been resolved in the past for both precast hollow core and one-way pan-joist systems. While I couldn't find any relevant details or discussion for pan-joists, I found plenty for hollow core slab systems. Unfortunately, if the precast details addressed these issues at all, they did so only for initial dead load deflections (camber), not for live load or long term deflections.
With regard to this issue, PCI's Manual for the Design of Hollow Core Slabs says:
The effect of different vertical stiffnesses may be accounted for by:
1. Determining that distress will not affect the strength or performance of the system,
2. Locating vertically rigid connections near the slab supports where vertical movement is minimized, or
3. Providing allowance for vertical movement in the connection detail.
How have others been dealing with this? Part of my concern is that the "joist" members are closely spaced and no one joist is capable of supporting all that much load. If I say that the topping slab is able to span perpendicularly to the joists for a distance that justifies allowing the joists to "hang up" against the wall, that topping slab will be spanning to a joist member that likely cannot support the additional tributary load.
Thanks for your help.
Kootenay Kid