Hello,
I have CHW campus loop (4 chillers), that would like to shutdown one chiller during the highest power demand load (design days, when everyone has an AC going and the grid needs as much power as possible). Since my client is a big power client as well, they are trying to do their part, by killing a chiller.
Their old method is by closing each building CHW control valve by about 30% and having each building fend for itself. I disagree with this system, because the closest building may get the flow required, while the furthest building will be more than starved. I prefer to control the flow, and have everyone a little starved.
They do not have a tiertiery system, but rather CHW control valve in each buildign, which i disagree with, but is another post for another time.
My solution is to implement a CHW Demand Reduction Sequence, which basically is a two step process. One is increase the AHU DAT from 55 up to low 60's, while keeping a limit on thje dewpoint for humidity controls. This basically will trade fan energy for chiller energy. I havent done an energy analysis (and not sure how) but everything I read says you will get the most savings with the chiller.
The second step is to increase the zone setpoints from 1-5 degF, depending on the type of space. We expect the occupants to be slightly uncomfortable but not too uncomfortable for the one or two days.
Wondering if there were any other ideas out there? or if there are any issues you may have with my proposed solutions.
Thanks.
when the grid is being would be when the AC is required the most)
knowledge is power
I have CHW campus loop (4 chillers), that would like to shutdown one chiller during the highest power demand load (design days, when everyone has an AC going and the grid needs as much power as possible). Since my client is a big power client as well, they are trying to do their part, by killing a chiller.
Their old method is by closing each building CHW control valve by about 30% and having each building fend for itself. I disagree with this system, because the closest building may get the flow required, while the furthest building will be more than starved. I prefer to control the flow, and have everyone a little starved.
They do not have a tiertiery system, but rather CHW control valve in each buildign, which i disagree with, but is another post for another time.
My solution is to implement a CHW Demand Reduction Sequence, which basically is a two step process. One is increase the AHU DAT from 55 up to low 60's, while keeping a limit on thje dewpoint for humidity controls. This basically will trade fan energy for chiller energy. I havent done an energy analysis (and not sure how) but everything I read says you will get the most savings with the chiller.
The second step is to increase the zone setpoints from 1-5 degF, depending on the type of space. We expect the occupants to be slightly uncomfortable but not too uncomfortable for the one or two days.
Wondering if there were any other ideas out there? or if there are any issues you may have with my proposed solutions.
Thanks.