KootK said:In many practical situations, appropriate joint modelling has more to do with what's going with the members coming into the joint than with the restraint offered by the joint itself.
271828 said:If the column has a much higher MOI, then the column/beam combo is looking more like a moment frame, so again I'd start taking the continuity more seriously.
Celt83 said:For what it’s worth AISC Design Guide 24 does call this a moment connection and advises the use of stiffeners or a joist brace connection directly to the column to restrain out of plane column buckling.
Kootk said:The most common place where I feel that this occasionally warrants some non-"by inspection" level consideration is at perimeter "wind columns".
Celt83 said:For what it’s worth AISC Design Guide 24 does call this a moment connection and advises the use of stiffeners or a joist brace connection directly to the column to restrain out of plane column buckling.
Celt83 said:Section 4.2 of Design Guide 24
Celt83 said:The title of chapter 4 is Moment Connections and the first worked example is a beam over hss connection with applied moment.
KootK said:In many practical situations, appropriate joint modelling has more to do with what's going with the members coming into the joint than with the restraint offered by the joint itself.
SE2607 said:KootK - If the beam rotates at the top of the column, and the column is properly attached to the beam, isn't the top of the column going to rotate the same amount?
KootK said:Right, but I would interpret those things to mean that such connections can be used to transfer moment when desired. I would not interpret them to mean that any particular part of the system must be designed for moment when that connection type is used.
KootK said:joint restraint is necessary but not sufficient to draw appreciable moment to a joint.
SE2607 said:If the top of the column rotates and is restraint in any way (pinned, fixed), then there is a moment in the column at the top.
phamENG said:It sounds like you're trying to have your cake and eat it too, KootK.
KootK said:Right, but I would interpret those things to mean that such connections can be used to transfer moment when desired. I would not interpret them to mean that any particular part of the system must be designed for moment when that connection type is used.
KootK said:Joint restraint is necessary but not sufficient to draw appreciable moment to a joint.
phamENG said:BUT...we can proportion the members of the system such that the moment that we have to design for is small.
phanENG said:So the joint itself must be designed for the moment.
SE2607 said:MSL - when you write "...it doesn't matter whether it's pinned or fixed, does it?..."(yeah, I forgot how to quote. Next time someone schools me on that, I'll write it down. At the time, it was so obvious, I said to myself "I'll remember that."), if the connection is pinned, then there is rotation in the beam at that point. Are you saying the top of the column does not rotate?
Was outright failure (collapse) ever even being debated?DaveAtkins said:Another thing to consider is the likely failure mode for this type of structure.