True. I can't argue with that, you are correct. It was a quick model to show the point graphically. As far as base connections go I agree, I have also argued and modelled the behaviour of typical 'pinned' base connections which can readily be semi-rigid or rigidly connected to the footing. The footing however might behave in a pinned fashion for higher loads.Celt83 said:Human:
To be fair if you are going to model the top beam/column connection rigid then should probably also model the column base connection as rigid or a rotational spring. Also should probably have a rigid end offset between the beam and column to move the attachment to the beam base, the stiffeners will take care of the panel zone deformations.
I disagree. Just because minimal moment is being transferred (which is the corollary of minimal change in deflection) doesn't necessarily mean CURVATURE isn't being transferred. It is this curvature and the associated column deflections that are the issue I have been highlighting. It is also and issue I've seen in the field with my eyes, as has WesternJeb. It does not look impressive when the column has visible bend under simple dead load.Celt83 said:Your model deflections for the beam are actually quite similar so it would seem that in isolation designing the beam as pin-pin would be accurate.
I perform the envelope approach if I'm at all concerned. Regarding the column capacity, I've explored in depth previously on eng-tips, most of the time the what you lose in capacity in additional column moments you gain in capacity in reduced effective length.Celt83 said:Not trying to discount the concerns with the column response and like the envelope approach.
I'd normally design things as pinned and quickly move on. I have no problem with that approach without rigorous analysis only if you are "eyes wide open" regard the assumptions you are making and the potential consequences. Us structural engineers make simplifying assumptions all the time, sometimes knowingly sometimes unknowingly. But if we make such an assumption in the wrong circumstance then there can be issues. This is where engineering judgment comes into things.milkshakelake said:@human909 If it were a column under a cantilever beam for a balcony or some small load, would you still apply a rigorous analysis or let it go as pinned?
X4Vier said:Cap plate for Pipe - How can release moments?
Kootk said:In many of the scenarios where these types of connections are used, the same connection that exerts a bit of moment on the columns will also serve to rotationally restrain the columns at the joint. So K=0.7-ish rather than K=1.0 or whatever.
KootK said:Recognize that the governing mode of failure for many gravity columns is not cross sectional stress but, rather, inelastic buckling.
Tomfh said:If we have a true pin joint, and we have ductile members, can we genuinely weaken the structure by locking the joint?
Tomfh said:Perhaps it's fine after all - with any induced moment being more than made up for by the additional fixity?
Tomfh said:If we have a true pin joint, and we have ductile members, can we genuinely weaken the structure by locking the joint?
SE2607 said:Unfortunately (or maybe fortunately), our work is reviewed by others and we have to defend the design...
milkshakelake said:When you have combined axial compression w/ slender buckling and flexure, with some columns being proportioned barely enough for bending (say HSS4x4), the bending will overtake the buckling.
Yes and no. As I said before normally the benefit of reduced effective length can offset the increase demand from the moment. However this really is a case by case basis, if you are close to the line then a rigid joint can put you over the line.Tomfh said:If we have a true pin joint, and we have ductile members, can we genuinely weaken the structure by locking the joint?
phamENG said:too bad we're all fixed in our ways...
271828 said:FWIW every firm I've worked for (reputable firms) would design the members as if there's a hinge at the top of the column and create a non fully-restrained moment connection by using:
1. a non-thick cap plate;
2. non-large bolts; and
3. one set of stiffeners at the column centerline.
If the detail had a beefy cap plate, large bolts, and two sets of stiffeners like shown in the OP, then I might take the continuity more seriously.