Braced Frame Footing - Lateral EQ load or Wind load

Status
Not open for further replies.

hello12345hello

Structural
Apr 25, 2011
50
Hello,

I have braced frame with column footings. I have 50 kip lateral shear. Both footings are isolated. I will check footing for sliding using soil friction and passive pressure. I will assume footing takes all lateral shear, slab on grade is not count.
Now question is to check overturning for footing i have to add moment due to hori. load.
Say my footing is 36 in deep. so i have (50kip*3 ft = 150 kip ft additional moment. do i have to count that to check for soil pressure?
Now say if i will add grade beam between two braced frame footing, then to check the footing do i have to consider this additional moment.
 
Replies continue below

Recommended for you

If you have a grade beam attaching the footings, then design the footing for axial and shear only and design the grade beam for the end moment of V*h/2.
 
And you do have to consider the extra 3 feet of footing depth to the bottom of the footing to get the correct soil pressure.

Mike McCann
MMC Engineering
Motto: KISS
Motivation: Don't ask
 
Lion,

Can you please explain design for axial vertical load and hori shear load means?
If i am understanding correct i will check footing for max vertical load and check for sliding against hor. shear load. I will check grade beam for moment = hori. load*ht./2 at the end of grade beam.?
And to check overturning consider min. vertical load (uplift)only.
Moment = pmin*footing width/2.
Thank you


 