ACI 318-14 said:At simple supports, at least one-third of the maximum positive moment reinforcement shall extend along the slab bottom into the support, except for precast slabs where such reinforcement shall extend at least to the center of the bearing length.
ACI 318-14 said:At other supports, at least one-fourth of the maximum positive moment reinforcement shall extend along the slab bottom into the support at least 6 in.
ACI 318-14 said:Positive moment reinforcement shall extend to the edge of slab and have embedment, straight or hooked, at least 6 in. into spandrel beams, columns, or walls
ACI 318-14 said:At least two of the column strip bottom bars or wires in each direction shall pass within the region bounded by the longitudinal reinforcement of the column and shall be anchored at exterior supports.
There indeed are some functions in ACI 318 for development length of reinforcement.centondollar said:Thank you very much.
jayrod12 said:Is there any clear requirement for splice of temperature-shrinkage reinforcement?
jayrod12 said:You are right. Because I am working at site now, so I am always eager to learn some conceprts.