Beam Reinforcement Calculation 2
Nick6781
CA
Let's say I need to use a web plate instead of a flange cover plate (I know...) to reinforce a beam. How do I calculate the required weld to ensure the section acts compositely? The shear flow equation gives the shear along a horizontal plane, but in this case, the faying surface is vertical. I can't quite wrap my head around it.
Thanks HTURKAK, I see it now. Very neat!
Once again, I apologize to everyone for prolonging this discussion to so many posts. I will try to keep quiet on this subject from here on.
👋 BAretired
No need to apologise, now I'll take the blame for continuing the discussion. ;)
It is nuanced because the VQ/I is an inherently correct formula from theoretical fundamentals. Though how it understood and applied is more nuanced than people can realise. For example, from a calculative perspective there is nothing in the calculation telling WHERE the shear needs to be transferred and there is nothing even to require that the elements be contiguous (connected or each other).
Furthermore there is NOTHING in that formula that involves "picking a point". So this notion of only calculating shear flow at a point and especially only calculating Q in one direction (eg upward or downwards) is fundamentally flawed no matter what a textbook says. (Though typically the boundary between two areas becomes the point or plane where one is choosing to consider the shear flow.)
EG;
This section on the left still has a calculable V, Q & I. You can calculate the shear flow required between A & B but all that tells you is that VQ/I shear must be flowing between A and B, even though there is no obvious way it can nor an obvious way for V to be identical and thus one might rightly question that it is a indeed a single section. So we can fix that.
Now we are looking at something a little more familiar. We can calculate V,Q,I and work at the shear demand at any point. we want. That break between section A and B can be anywhere we choose. Also we can work out Q on whichever area we choose. The normal way of calculating the above would be to calculate the Q of section B. But you can just as easily calculate the Q of section A and get the same answer. If we choose to calculate the Q for section A we get a value of ZERO for the web of A and the value of Q of section A flange is equal to the B flange. So that all checks out, something would be amiss if the VQ/I gave different results if you choose the opposite section.
Likewise we can go nuts calculating the shear flow in this double-I section however you want. But if you choose to calculate Q of (A&B) or (A' & B') then you will get Q=0. You can call it a compound section as much as you want. You can weld those flanges together if you choose. However as long as you can ensure that V is equal then the VQ/I=0 and there is no shear flow. The original example is no different. There is no shear flow between the plates and the beam because Q =0
I hope this example above will convince you against the perverse notion of picking a point and only calculating Q above or below it. If I was going to size the welds for section C I'd consider ALL of the area of C to calculate Q, not just the bit 'above' my weld.
Oh, and there is one more method of analysis that I found really useful graphically and match up to calculated results within a 5%.
I modelled two beams
-200mm deep, 100mm wide flange, 10mm thick web and flange, point loaded with 100kN, 2m long
The top beam exactly matches hand calcs as the section is drawn perfectly. The lower one is slightly out because it is actually made of a grillage of members (20x10mm).
Because this is a grillage you can readily see the shear flow in discrete elements. A grillage of 1D elements is a poor man's 2D or 3D FEA. But it is often more interpretable and user friendly than FEA.
You can measure and visually see the shear flow and also the shear lag around the supports. My measured value is 5.63kN of shear per 20mm, the hand calculated value is 5.91kN. So 5% out, but it isn't a perfect model but it is good to play around with and observe the shear flow. I also found it quite satisfying to see the shear flow at the top add up in 20mm segments to equal the total axial load in the flanges at centre. Again something you should expect but satisfying to see it incrementally and visually.
I also modelled the example of the I beam with plates. The result is as expected, no shear flow as there is no stress/strain differential between the plates and the web. If people are interested I can post more. But I think this post has been long enough.
👋 BAretired
EG;
Great post. The only thing left for you to do here is to grab a W-shape, a few plates, and start building a model for us :LOL:
Thanks. The one thing I did leave out is referring to NET or TOTAL shear. I would think by now this would be clear, but I've made the mistake many times of thinking things were clear when they are not.
If you break up section C from section A below and calculate QV/I=0 then you would be correct but it wouldn't do you much good if you were trying to size up welds between C & A. Correct in that the NET/TOTAL shear between section C and A is zero, but incorrect because you do have shear equal and opposite shear at the boundaries between A&C.
Again in the situation of the plates you don't have this issue because the plates are a continue piece so the shear nets out. As long as deflection is the same then the stress/strain gradient between the web and the plates is zero so even if you weld/glue/bolt there is no longitudinal shear flow.
My understanding for the weld calculation below is to find the Q value for the upper or lower green shape.
The upper fillet welds must resist a shear flow of VQ/I where Q is taken for the upper green outline.
Similarly, the lower welds resist VQ/I where Q is for the lower green outline.
I don’t believe shear flow is 0 at the C/A interface it’s my understanding that you can look at the vertical shear plane at C/A and use the Q as the first moment of area for the C area about the composite centroid sim to the below pulled from Mechanics of Materials 7th edition by Beer:
Agreed 100%.
Sorry, I thought the point being made was fairly clear that calculating the total area C wouldn't be useful. You would need to calculate the Q area separately as you both point out.
Calculating them both together gives you the NET shear flow of the top and bottom segments which is pretty unhelpful in this example.
It is 0 when you add the value of the TWO C/A interfaces. They are equal in magnitude but opposite in sign. Adding them or calculating the NET shear flow into C is pretty unhelpful but it is NOT an invalid calculation. I'm have just been bring up examples like this to emphasise the SIGNED nature of Q.
Agreed 100%.
Great!
We have total agreement. Thanks human909.
I'm back. Good discussions so far.
In the flange, the direction of the shear flow lies in a horizontal plane. I'm supporting human909's argument with the diagram below:
Regarding the textbook explanations:
In my beam, the horizontal stress induced by the differential moment in the plates above and below the neutral axis cancels out, as I mentioned earlier. Therefore, there is no horizontal shear flow between the plates and the beam.
In addition, analyzing a cube from the plate should yield the same conclusion, there shouldn't be shear flow on the front and back surfaces of the cube.
In summary, I agree with human909's point—only vertical shear transfer needs to be considered, so welds are required for vertical shear only.
Nick6781 said:
Only vertical shear transfer needs to be considered, so welds are required for vertical shear only.
That is simply not true. Your own diagrams show otherwise.
Has Koot gotten into this one yet? I haven't read the four pages yet.
No, I've been waiting for him to show up. Maybe he is busy, or bored with the topic. He did provide input in the previous thread linked largely along similar lines of argument as what I have put forward.