Use of ties & vertical rebar reinforcement to help with Concrete breakout strength of shear lug
oengineer
I have a shear lug/key that I am working on designing using Hilti Profis for a concrete pedestal. However, Profis is telling me that the shear lug is failing in concrete break out strength. My pedestal is 44"x44" & 40" tall, with (28)-#8 vertical rebars (see images). The tie reinf. is also shown in the images.
My shear forces acting on the pedestal are the following: Horizontal load on Pedestal (Hx) = 143.8 kips & Horizontal load on Pedestal (Hz) = 225.6 kips
If the pedestal itself has been designed to resist the shear forces based on the pedestal section, concrete strength, vertical rebar & all the ties....would it be safe to consider that the verti. reinf. & ties would be adequate to prevent concrete break out for the shear lug/key?
Suggestions/comments are appreciated.
I dont think it's enough to stay the pedestal is strong enough to resist the total shear, otherwise you could end up with some strange designs with the shear lug less than 2 inches from the edge etc.
Check whatever code/recommended practice you are following to see if there is a comment on concrete breakout check not being required/a valid failure mode if correctly placed rebar is present. Many codes do discuss the effect of correctly placed rebar on breakout and your code might give a spacing or other requirement to satisfy that condition. then it might be OK by inspection.
Hilti profis also allows you to add rebar in the model for some situations (and so switches the concrete breakout failure mode check to rebar strut and tie checks) , i don't know if profis allows the simultaneous use of a shear lug and explicit rebar. If it doesnt then it's likely an engine limitation rather than a design limitation.
Hilti presentation on profis rebar checks
There needs to be some check that covers whether or not your anticipated lug breakout frustum convincingly engages the shear reinforcement in the pier. In practice, this is analogous to doing a strut and tie design and checking that your strut angles are sensible / permissable.
The 3rd Edition of AISC's design guide on base plate anchorage now incorporates the latest research and is massive improvement over the previous two editions of the guide. I'd get your hands on a copy of that if you haven't already.
I am using ACI 318-19. I am looking in this code to find use of supplementary reinforcement to help with concrete breakout for shear lugs.
The pedestal capacity aside, you may want to look more closely at the constructabilty of what is proposed. #8 hair-pins will have an inside bend radius of not less than 6Db. Couple that with the anchor bolts, shear lug, and all the ties and I think you'll have lots of pieces colliding with each other.
Oengineer, supplementary reinforcement will help your breakout capacity by a couple %.
You should look into anchor reinforcement rather than supplementary reinforcement.
As an alternative to a strut and tie model, you can count on the ties as anchor reinforcement if they are developed on both sides of the breakout cone:
I wouldn't count on any ties beyond the first three layers.
Also, as a rule of thumb I would only count 50% of the ties as effective given that some of them will have 135 degree hooks that limit the capacity in the tie.
What other anchor reinforcement should I look into besides the ties currently shown in the images I have provided?
What about friction force?
The shear force 225 kips is a substantial figure and i checked the break out cone capacity of the concrete pedestal . Unfortunately It is less than 100kips for Fc =3000 psi.
The additional reinf. ( in this case closed stirrups ) is a requirement if shear lug is used or in case of high seismic zones.
I have also checked the supplementary reinf . roughly and reinf. amount is also not enough. ( i estimated more than 6 in2.).
The basic principle is shear reinforcement shall be designed to carry the entire shear load, without considering any contribution from concrete.
I have attached the best practice for Anchor Bolt Design and Installation
SABP-Q-001 to see the different type reinforcement options. (this document is free on the web
The shear force 225 kips is a substantial figure and i checked the break out cone capacity of concrete . Unfortunately It is less than 100kips for Fc =3000 psi.
The additional reinf. ( in this case closed stirrups ) is a requirement if shear lug is used or in high seismic zones.
Thank you for this check. However, please note that the concrete strength is f'c=4000 psi for this pedestal.
..... However, please note that the concrete strength is f'c=4000 psi for this pedestal.
If concrete strength is f'c=4000 psi , break out cone capacity of the concrete pedestal will increase only 15%.You need to do more. Some options, can you weld the embedded plate to the anchors? Can you increase the size of the pedestal?
I do not believe welded the anchors to the base plate is an option. Do you have a suggestion on how much the pedestal should be increased to solve the concrete break out? Do the (28) - #8 vert rebars help with the shear for the concrete break out?
Are there any other things that could be done to resolve this issue?
- Filling the annular space btw base plate hole and anchor rod with welding is an option to engage all the four anchors. Sometimes, washers are welded to the base plate as an alternative.
- Pedestal size could be 4 ftX 4 ft. ( i understood the size 3.0 ft X 3.0 ft but 3 ft 8 in size still not enough)
- the (28) - #8 vert rebars will help but closed form stirrups are the key reinf. in this case.
Apparently the shearkey is welded to 1 in embedded plate and there is another base plate . How the base plate connected to embedded plate and how the shear force 225 kips transferred to shear key is not clear.
Could you extend the steel frame down to the footing and encase in concrete.
Is there any type of additional reinforcement that could be added to help the shear key for breakout strength?
