Greetings.
I haven been looking at all various threads about VFD cable lengths and the insightful responses from all the VFD gurus in this site, however, almost all of these topics were focused at L.V VFDs and very few had discussed this subject in M.V domain.
I have just joined a new company and was briefed to follow an on-going project of ours that involves an MV VFD for our 11kV, 2300kW Export Pump. The unit was already selected before I joined and it's being shipped as we speak; However, upon reading the vendor documents and datasheet, I became concerned that the 500m distance between the VFD room and the Export pump might create a set of issues which might end-up damaging the Export Pump so I raised this concern to the vendor technical team and they assured me that they selected VFD has carefully selected parameters to mitigate any of cable distance issues that might arise.
I'll attach the parameters below and continue addressing my points of concerns:
------------------------------------------------------------
TYPE OF VFD INVERTER (LCI/VSI) : VSI
NUMBER OF PULSES - SUPPLY SIDE/MOTOR SIDE: 54 PULSE / 54 PULSE
INPUT POWER FACTOR AT VFD: 0.85
SPEED RANGE: 1&~150%
POWER CABLE LENGTH FROM VFD PANEL TO MOTOR: COMPLY
HARMONIC STUDY (OVERALL / LIMITED TO EACH DRIVE): COMPLY
CAPACITANCE WITH SERIES INDUCTANCE: Provides avoidance of 3 resonance point
frequencies
REACTOR / FILTERS: NO REACTOR / FILTERS IN VFD
HARMONIC FILTER REQUIRED (YES / NO) : NO
SEPARATELY MOUNTED REACTOR REQUIRED (YES / NO): NO
SEMICONDUCTOR DEVICES (DIODE / THYRISTOR / IGBT / IGC: IGBT
CONVERTER CONFIGURATION (3-PH UNCONTROLLED / 3-PH SEMI: 3-PH UNCONTROLLED
SEMICONDUCTORS PER BRANCH: 36
NO. OF PULSE: 54
TOTAL INPUT RMS CURRENT (IS) (AT 100%,75%,50% LOAD) : 577,433,288A
% CURRENT THD (AT 100%,75%,50% LOAD) : 3%,3.5%,5%,7%
FUMNDAMENTAL POWER FACTOR (DPF): 0.92,0.92,0.92
CURRENT HARMONIC PROFIE :
5th: 2.2A @ 100% DEG
7th: 1.06A @ 100% DEG
11th: 1.42A @ 100% DEG
13th: 1.36A @ 100% DEG
17th: 0.11A @ 100% DEG
19th: 0.07A @ 100% DEG
23th: 0.03A @ 100% DEG
25th: 0.03A @ 100% DEG
DC LINK VOLTAGE: 1800v
MAX. DC LINK CURRENT : 380A
INPUT REACTOR : NO
DC LINK REACTOR/CAPACITOR : NO
SWITCHING FREQUENCY RANGE: 800Hz-2000Hz
Voltage THD: 3%
CURRENT THD: 3%
VFD OUTPUT VOLTAGE SURGE (dv/dt) AT MOTOR TERMINAL:
A:PH-PH : 1kV(Peak/sec.)
B:PH-GND: 0.6kV(Peak/Sec.)
-----------------------------------------------------------------------------
My concern is how the vendor achieved the stated values of 1kV,0.6kV for such long cable length without the use of reactors/filters?
I haven been looking at all various threads about VFD cable lengths and the insightful responses from all the VFD gurus in this site, however, almost all of these topics were focused at L.V VFDs and very few had discussed this subject in M.V domain.
I have just joined a new company and was briefed to follow an on-going project of ours that involves an MV VFD for our 11kV, 2300kW Export Pump. The unit was already selected before I joined and it's being shipped as we speak; However, upon reading the vendor documents and datasheet, I became concerned that the 500m distance between the VFD room and the Export pump might create a set of issues which might end-up damaging the Export Pump so I raised this concern to the vendor technical team and they assured me that they selected VFD has carefully selected parameters to mitigate any of cable distance issues that might arise.
I'll attach the parameters below and continue addressing my points of concerns:
------------------------------------------------------------
TYPE OF VFD INVERTER (LCI/VSI) : VSI
NUMBER OF PULSES - SUPPLY SIDE/MOTOR SIDE: 54 PULSE / 54 PULSE
INPUT POWER FACTOR AT VFD: 0.85
SPEED RANGE: 1&~150%
POWER CABLE LENGTH FROM VFD PANEL TO MOTOR: COMPLY
HARMONIC STUDY (OVERALL / LIMITED TO EACH DRIVE): COMPLY
CAPACITANCE WITH SERIES INDUCTANCE: Provides avoidance of 3 resonance point
frequencies
REACTOR / FILTERS: NO REACTOR / FILTERS IN VFD
HARMONIC FILTER REQUIRED (YES / NO) : NO
SEPARATELY MOUNTED REACTOR REQUIRED (YES / NO): NO
SEMICONDUCTOR DEVICES (DIODE / THYRISTOR / IGBT / IGC: IGBT
CONVERTER CONFIGURATION (3-PH UNCONTROLLED / 3-PH SEMI: 3-PH UNCONTROLLED
SEMICONDUCTORS PER BRANCH: 36
NO. OF PULSE: 54
TOTAL INPUT RMS CURRENT (IS) (AT 100%,75%,50% LOAD) : 577,433,288A
% CURRENT THD (AT 100%,75%,50% LOAD) : 3%,3.5%,5%,7%
FUMNDAMENTAL POWER FACTOR (DPF): 0.92,0.92,0.92
CURRENT HARMONIC PROFIE :
5th: 2.2A @ 100% DEG
7th: 1.06A @ 100% DEG
11th: 1.42A @ 100% DEG
13th: 1.36A @ 100% DEG
17th: 0.11A @ 100% DEG
19th: 0.07A @ 100% DEG
23th: 0.03A @ 100% DEG
25th: 0.03A @ 100% DEG
DC LINK VOLTAGE: 1800v
MAX. DC LINK CURRENT : 380A
INPUT REACTOR : NO
DC LINK REACTOR/CAPACITOR : NO
SWITCHING FREQUENCY RANGE: 800Hz-2000Hz
Voltage THD: 3%
CURRENT THD: 3%
VFD OUTPUT VOLTAGE SURGE (dv/dt) AT MOTOR TERMINAL:
A:PH-PH : 1kV(Peak/sec.)
B:PH-GND: 0.6kV(Peak/Sec.)
-----------------------------------------------------------------------------
My concern is how the vendor achieved the stated values of 1kV,0.6kV for such long cable length without the use of reactors/filters?
RE: MV VFD Cable Length Concern
RE: MV VFD Cable Length Concern
54 pulse sounds like a cascaded H-bridge, but the part about DC link voltage doesn't seem to correspond with one. Cascaded H-bridge topologies don't have many issues with long cable lengths.
RE: MV VFD Cable Length Concern
1800V DC bus indicate cascaded H bridge, a multilevel inverter or some special topology.
For a VSI cable lenght it's problem even here switching frequency is not high and maybe dv/dt is limited by switching devices/firing control.
I thing is better to request manufacturer at least a simulation for your setup and frequency range / acceleration ramp with motor load from 0 to max allowed.
RE: MV VFD Cable Length Concern
https://files.engineering.com/getfile.aspx?folder=...
RE: MV VFD Cable Length Concern
If it was conducted it should be a deliverable. It may have the details regarding how much ringing should be expected.
There are two items to look at
- resonance resulting from dv/dt from the leading edge of the square wave,
- resonance resulting from the drive excitation frequency.
A 54 pulse drive output transformer could damp the resonance, depending on transformer design. This is about the limit of my expertise, going further than the vendors resonance report requires experts in fundamentals of EE.RE: MV VFD Cable Length Concern
RE: MV VFD Cable Length Concern
I'll be sure to return and verify the data once the VFD arrives from China and will be sure to make a separate post about my findings if any arises.
Regards.
RE: MV VFD Cable Length Concern
Also note that at lower loads, the THD (current) content goes up significantly, as expected, to around 7% at one-quarter load. This may show up as a different "max" harmonic profile compared to the full-load case - which might need additional mitigation.
Lastly - the drive has three "blocked" bands where known resonance may occur based on the system data provided for the drive vendor to quote (presumably the cable type, length of run, and machine impedance connected at the far end). There is also provision within the software to add some (unsure how many) other "blocked" operating points, just in case things aren't quite exactly what the drawings show.
Converting energy to motion for more than half a century
RE: MV VFD Cable Length Concern