Greetings.
I haven been looking at all various threads about VFD cable lengths and the insightful responses from all the VFD gurus in this site, however, almost all of these topics were focused at L.V VFDs and very few had discussed this subject in M.V domain.
I have just joined a new company and was briefed to follow an on-going project of ours that involves an MV VFD for our 11kV, 2300kW Export Pump. The unit was already selected before I joined and it's being shipped as we speak; However, upon reading the vendor documents and datasheet, I became concerned that the 500m distance between the VFD room and the Export pump might create a set of issues which might end-up damaging the Export Pump so I raised this concern to the vendor technical team and they assured me that they selected VFD has carefully selected parameters to mitigate any of cable distance issues that might arise.
I'll attach the parameters below and continue addressing my points of concerns:
TYPE OF VFD INVERTER (LCI/VSI) : VSI
NUMBER OF PULSES - SUPPLY SIDE/MOTOR SIDE: 54 PULSE / 54 PULSE
INPUT POWER FACTOR AT VFD: 0.85
SPEED RANGE: 1&~150%
POWER CABLE LENGTH FROM VFD PANEL TO MOTOR: COMPLY
HARMONIC STUDY (OVERALL / LIMITED TO EACH DRIVE): COMPLY
CAPACITANCE WITH SERIES INDUCTANCE: Provides avoidance of 3 resonance point
frequencies
REACTOR / FILTERS: NO REACTOR / FILTERS IN VFD
HARMONIC FILTER REQUIRED (YES / NO) : NO
SEPARATELY MOUNTED REACTOR REQUIRED (YES / NO): NO
SEMICONDUCTOR DEVICES (DIODE / THYRISTOR / IGBT / IGC: IGBT
CONVERTER CONFIGURATION (3-PH UNCONTROLLED / 3-PH SEMI: 3-PH UNCONTROLLED
SEMICONDUCTORS PER BRANCH: 36
NO. OF PULSE: 54
TOTAL INPUT RMS CURRENT (IS) (AT 100%,75%,50% LOAD) : 577,433,288A
% CURRENT THD (AT 100%,75%,50% LOAD) : 3%,3.5%,5%,7%
FUMNDAMENTAL POWER FACTOR (DPF): 0.92,0.92,0.92
CURRENT HARMONIC PROFIE :
5th: 2.2A @ 100% DEG
7th: 1.06A @ 100% DEG
11th: 1.42A @ 100% DEG
13th: 1.36A @ 100% DEG
17th: 0.11A @ 100% DEG
19th: 0.07A @ 100% DEG
23th: 0.03A @ 100% DEG
25th: 0.03A @ 100% DEG
DC LINK VOLTAGE: 1800v
MAX. DC LINK CURRENT : 380A
INPUT REACTOR : NO
DC LINK REACTOR/CAPACITOR : NO
SWITCHING FREQUENCY RANGE: 800Hz-2000Hz
Voltage THD: 3%
CURRENT THD: 3%
VFD OUTPUT VOLTAGE SURGE (dv/dt) AT MOTOR TERMINAL:
A
H-PH : 1kV(Peak/sec.)
B
H-GND: 0.6kV(Peak/Sec.)
My concern is how the vendor achieved the stated values of 1kV,0.6kV for such long cable length without the use of reactors/filters?