VFD(VSD) on sluice gates 3
CuriousElectron
Hi All,
I had a question - I'm seeing Variable frequency drives or variable speed drives being used on sluice gates (vertical slide gates) to drive gate motor actuator. Why is the reason behind it? Why not use a standard FVNR starter instead. These gates are rated at 3 HP to 5 HP. I see they are used in project sites where 3 phase is not available, so those drives convert 1 phase 120VAC into 3 phase 240V. Is that the main reason, to be able specify a 3 phase motor instead of a 1 phase motor and have better means of control& longevity of the electric actuator?
Thank you.
EE
Three phase on a VFD versus a single phase motor;
Less points of failure on a three phase motor compared to a single phase motor.
Lower starting surge with a VFD.
More breakaway torque to overcome sticktion with a three phase motor compared to a single phase motor.
Even more breakaway torque to overcome sticktion with the torque boost feature of the VFD.
Also, simple reversing, which is more complex with single phase motors. With a VFD on a 3 phase motor, you just give it a reverse command, no contactors involved.
With Sensorless Vector Control, which is standard on most VFDs now, you can get full torque at the outset, you no longer need to use torque boost. But better than that, you can get a soft start from it, so less wear and tear on the gearbox of the weir gate.
Great question! Here’s why VFDs are preferred for sluice gates:
Phase Conversion: VFDs can convert single-phase 120VAC into three-phase 240V, allowing the use of more efficient and reliable three-phase motors in locations where three-phase power is unavailable.
Speed and Torque Control: VFDs offer precise control over motor speed, making it ideal for controlling gate positions. They also provide higher breakaway torque to overcome sticktion when compared to single-phase motors.
Soft Start: VFDs reduce inrush current at startup, minimizing electrical and mechanical stress, and extending the life of both the motor and actuator.
Torque Boost: The torque boost feature in a VFD further enhances breakaway torque, ensuring smoother and more reliable operation of the gate.
In short, VFDs provide better control, efficiency, and motor protection, making them the ideal choice for this application.
AI generated?
I could see adding VFDs on single phase systems to allow for 3 phase motors would be a good practice. The max torque on a gate would be closed with the full force of water behind it, and single phase motors don’t have great starting torque. I have a feeling a smaller VFD and 3 phase motor would be significantly cheaper than installing a single phase motor large enough to overcome the starting torque of the gate.
I work at a company that has two hydroelectric dams and haven’t heard of any push yet to add VFDs to spillgate motors in the industry. We are actually currently reviewing designs to redo the entire top of dam including 12 new spillgates and spillgate mechanisms and there has been no suggestion thus far of using VFDs, but working at a hydroelectric dam we do have plenty of 3 phase power…
You probably know this Casey, but I will throw it out for others.
The best motor for the high starting torque demand of a spillgate would ne a design "D" motor, but I don't think that design "D"motors are an off the shelf item. I see than on shears,and punch presses but they are part of the machine package and I suspect that they are a special build for the machine manufacturers.
A design "D" is not efficient but has a torque curve starting at about 280% at locked rotor, decreasing from there as the speed increases.
The common, design "B" motor has a locked rotor torque of about 150% of full load torque. That drops to about 120% torque at around 20% speed and then increases to about 190% torque at about 85% or 90% speed.
With a VFD and a suitable acceleration ramp combined with current limit the design "B" motor is capable of the 190% torque across the whole speed range.
When the VFD output frequency is set so that the rotor frequency is maintained at about 2 1/2 times slip frequency as the motor accelerates, the torque will be at about maximum and above the DOL starting torque.
Single phase to three phase at the same voltage level seems a heck of a lot more doable that single phase to three phase at twice the voltage level. How is a DC bus fed at 120 VAC going to have enough oomph to fire at 240V phase-phase?
There is a special “voltage doubler” circuit added to the front end of the drive that boosts the DC from 165VDC to 330VDC. So as far as the inverter portion does, it’s no different.
The voltage doubler is typically limited to about 1-1/2HP max, but only because after that, it becomes significantly less expensive to just use a small transformer.