LTB if support is at the load?
3

LTB if support is at the load?

LTB if support is at the load?

(OP)
I have a long, simply supported beam with a single load at the center (like a fixed gantry hoist). It seems like if I provide full lateral support at the ends and the load point, that I wouldn't have to make any concessions for lateral torsional buckling. Is there any justification for this in AISC?

RE: LTB if support is at the load?

You change the unbraced length from L to L/2. If your beam is controlled by LTB or not depends on the section and the unbraced length. Just by virtue of bracing the point load location doesn't mean LTB isn't a limit state.

RE: LTB if support is at the load?

I agree with driftLimiter.
You'd also have support for weak-axis loads from the brace-point

RE: LTB if support is at the load?

I agree with driftlimiter. The entire beam will see bending and therefore the top flange will see compression. The brace will keep it from laterally torsionally buckling at the mid point but if LTB controls along the top flange anywhere else the top flange is free to buckle.

RE: LTB if support is at the load?

(OP)
Thanks. I was having trouble picturing the ltb deformed shape.

RE: LTB if support is at the load?

Quote (Kilgore48)

provide full lateral support at the ends and the load point, that I wouldn't have to make any concessions for lateral torsional buckling.

Your instincts aren't too far off with that. While your setup doesn't preclude LTB, it is generally quite favorable to have bracing at the point of load application. If you do the k = L/2 evaluation with with an accurate assessment of Cb, I expect that your results will reflect this.

Your setup relies on the load itself to, effectively, brace the beam bottom flange laterally at the point of load application. I suspect that's fine but I wouldn't mind running an FEM buckling analysis on it for confirmation just the same. Or just run a real brace down to the bottom flange for good measure.

RE: LTB if support is at the load?

(OP)
Thanks, KootK. My sketch isn't exact, of course. I show bracing on the compression flange - isn't that all you need? It wouldn't be hard to brace the entire height, but I don't see any advantage.

RE: LTB if support is at the load?

Quote (Kilgore48)

I show bracing on the compression flange - isn't that all you need?

Usually? It's kind of a tricky question to answer that robustly.

Imagine if your beam were really the top chord supported steel joist below. Here, we can agree that the joist would roll over catastrophically, right? The bottom chord would kick out laterally?

Next, ask yourself, what about the your real beam prevents this same outcome? I would say that it's two things:

1) The beam bottom flange acting like a girt to restrain itself laterally at the point of load application. Calling this beam torsional resistance is just another perspective on the same thing.

2) The load being applied below the top flange such that a couple is formed that would tend to resist the bottom flange kicking out laterally. This you've probably got in spades too if I'm envisioning your situation correctly.

Both of these mechanisms are real, no doubt. But neither usually gets evaluated explicitly and neither is as "positive" as positive lateral bracing to the bottom flange would be. That's why , for something that feels as though it might be pretty high stakes, I wouldn't mind some positive lateral bracing to the bottom flange.

RE: LTB if support is at the load?

(OP)
Thanks, KootK!

RE: LTB if support is at the load?

Full brace is better but top flange lat brace gives most of the capacity. Btm flange load not much help with lat brace there already,

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close