Kilgore48 said:
I show bracing on the compression flange - isn't that all you need?
Usually? It's kind of a tricky question to answer that robustly.
Imagine if your beam were really the top chord supported steel joist below. Here, we can agree that the joist would roll over catastrophically, right? The bottom chord would kick out laterally?
Next, ask yourself, what about the your real beam prevents this same outcome? I would say that it's two things:
1) The beam bottom flange acting like a girt to restrain
itself laterally at the point of load application. Calling this beam torsional resistance is just another perspective on the same thing.
2) The load being applied below the top flange such that a couple is formed that would tend to resist the bottom flange kicking out laterally. This you've probably got in spades too if I'm envisioning your situation correctly.
Both of these mechanisms are real, no doubt. But neither usually gets evaluated explicitly and neither is as "positive" as positive lateral bracing to the bottom flange would be. That's why , for something that feels as though it might be pretty high stakes, I wouldn't mind some positive lateral bracing to the bottom flange.