Changing the Modbus-RTU slave address on Rockwell Micro 820
Changing the Modbus-RTU slave address on Rockwell Micro 820
(OP)
I am using a Rockwell Micro 820 configured as a Modbus-RTU slave device.
Is there a way for the user to change the slave address without giving him access to the application code?
Is there a way for the user to change the slave address without giving him access to the application code?
RE: Changing the Modbus-RTU slave address on Rockwell Micro 820
It sounds like it might do what you're asking:
RE: Changing the Modbus-RTU slave address on Rockwell Micro 820
I am now able to change the Modbus RTU unit addresses from the HMI or via jumpers on PLC inputs.
I was also able to use the same method to set the Ethernet IP address.
Thanks You!