Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Convert a 0-200 Microamp Signal for use in PLC?

Status
Not open for further replies.

doehl1

Electrical
Jul 2, 2007
41
I have an old turbine control system that uses black boxes for temperature and speed control. I'm trying to get the speed (passive Mag pick-up) and temperature signals (Type K Thermocouple) in to a PLC for monitoring. I think piggy backing off the Mag pick and taking the signal into a high speed counter card at the PLC should be straightforward.

The temperature signal is more complicated. There's only one Type K signal (wire) going straight to the black box. I'd rather not molest/piggyback the thermocouple signal (splitter has delays, drift, etc) so am looking at a 0-200 MICROamp output signal that is available off of the temp control black box (proportional to the input t/c signal) that I could use for monitoring. How in the world can I convert or get a 0-200 microamp signal in to a PLC?


 
Replies continue below

Recommended for you

Accuracy isn't too critical. 0.5% - 1.0% or better preferred. The 0-200 microamp signal is just for monitoring, not precise control.

 
Parallel the Type K thermocouple with a length Type K wire from the input on the black box into a commercial temperature transmitter which will give you a 4-20mA output that any PLC can handle. Transmitters are typically "2-wire, loop powered", meaning you also have to provide a 24Vdc power supply to power the transmitter, but that power runs over the 2 wires going to the transmitter.

I suggest isolated inputs on temperature transmitters, because many commercial thermocouple junctions are grounded and grounding can produce ground loop problems; an isolated transmitter input avoids that issue.

There are two categories of temperature transmitters - dumb and smart. The dumb transmitter is factory configured for some input range, say, 0-500 Deg F. with a corresponding proportional 4-20mA output.

The smart transmitter's input can be configured zero/span for the 4-20mA output. Problem is, unless you're in an industry where the software/modem or handheld programming communicator is readily available, then you're stuck buying and learning whatever gear is needed to set the range.

A dumb transmitter should be pre-ranged; my recommendation for a smart transmitter one is to find a vendor who will configure the range for you so you don't have deal with the configuration end.

It pays to physically label a field transmitter with its configured input range so the next guy knows what the 4-20mA output signal represents.
 