Changing the Modbus-RTU slave address on Rockwell Micro 820 1

Status
Not open for further replies.

rmore

Electrical
Feb 4, 2011
35
I am using a Rockwell Micro 820 configured as a Modbus-RTU slave device.

Is there a way for the user to change the slave address without giving him access to the application code?
 
Replies continue below

Recommended for you

Check out the RMCC (Run Mode Configuration Change) function described on pages 23-26 (pdf) of Micro820 Programmable Controllers User Manual

It sounds like it might do what you're asking:

Run_Mode_Configuration_Change_phozx0.jpg
 
That works. And it's fairly straightforward once the MSG_CIPGENERIC function is properly configured.

I am now able to change the Modbus RTU unit addresses from the HMI or via jumpers on PLC inputs.

I was also able to use the same method to set the Ethernet IP address.

Thanks You!
 