MWFRS and C&C dome external pressure coefficient

MWFRS and C&C dome external pressure coefficient

MWFRS and C&C dome external pressure coefficient

(OP)
Hello,

Please refer to following figures in ASCE 7-10.
1. Pg- 265, Figure 27.4-2, MWFRS Domed roofs
2. Pg-344, Figure 30.4-7, C&C Domed roofs

Usually components and cladding are designed for higher wind loads than the main wind-force resisting system. Why is it that the negative external pressure coefficient is higher for a MWFRS dome compared to C&C dome?

Regards,
Su

RE: MWFRS and C&C dome external pressure coefficient

One table is offering you Cp values.
The other is offering GCp values.

So if you include a 0.85 value for G in the MWFRS chart values this will reduce those loads a bit.
Looks like GCp for MWFRS then varies from 0.21 to 1.27 vs. the 0.9 for C&C overall.

Check out Eng-Tips Forum's Policies here:
FAQ731-376: Eng-Tips.com Forum Policies

RE: MWFRS and C&C dome external pressure coefficient

(OP)
Thanks for your response JAE.

Variable 'hd':
I have a case in which the domed roof is supported by vertical walls. The vertical walls are supported on top of the roof of a regular building. In my opinion, variable 'hd' in Figure 27.4-2 and 30.4-7 is the height of vertical walls using building roof top as the reference point. And the velocity pressure exposure coefficient is calculated using the height of dome top with reference to the ground level.

Do you think this interpretation of 'hd' is correct?

Regards,
Su

RE: MWFRS and C&C dome external pressure coefficient

I think you have to tread a bit careful with that.
The dome values given were probably derived with the assumption of a ground-supported dome, either on walls or not.

Putting a dome on top of a higher building seems to create a different sort of wind pressure condition as you have significant amounts of wind (on the main building below) "squirting" upward and over the roof and dome areas vs. an on-grade condition.

Sometimes with strange geometries, you have to look at ASCE 7's wind values in several views to get a potential range of values and then use your engineering judgement from there.

Alternatively you would go the wind tunnel route but that may not be an option for you here.

Check out Eng-Tips Forum's Policies here:
FAQ731-376: Eng-Tips.com Forum Policies

RE: MWFRS and C&C dome external pressure coefficient

(OP)
Thanks again JAE!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close