Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations SE2607 on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

C&C Wind Load on Open Building

Status
Not open for further replies.

davidfi

Structural
Sep 28, 2005
39
How does one determine the C&C wind load on walls of an open building? ASCE 7-16 Section 30.7 details how to calculate C&C loads on roofs, but not walls. Am I missing something?
 
Replies continue below

Recommended for you

Well open buildings typically don't have walls. Are you referring to wind on things like drop beams? I believe ASCE 7 says to treat them like inverted parapets.
 
The building is open one side and has a glass wall on the other side.
 
I'm pretty sure this would classify as partially enclosed, not open. An open building has >80% of the area of each wall open. Sounds like you just have one and the rest are closed. Sort of like a bus stop shelter?

It'll be based on the internal pressure coefficient for the building based on the enclosure classification, which would be +/-0.55 I would think.

 
Status
Not open for further replies.

Part and Inventory Search

Sponsor