Cripple Wall/Pony Wall Above Beam?

Cripple Wall/Pony Wall Above Beam?

Cripple Wall/Pony Wall Above Beam?

(OP)
In residential construction I seem to remember there being a prescriptive requirement to place pony walls underneath beams, not on top of them. This makes sense to me in that the by placing them above a beam it can form a hinge. But I can't find current requirement addressing this issue. If there is such a current requirement I would love to be able to point to it to avoid having to prove that it's anything other than just my opinion. Does anyone know of such? Or have any other comments on this topic? Thanks.

RE: Cripple Wall/Pony Wall Above Beam?

Regardless of code, it depends on the length of the beam, its section properties, the load and if the beam is braced laterally by any other framing.
That being said, I rarely see an issue with beams with unbraced tops in residential construction.

RE: Cripple Wall/Pony Wall Above Beam?

(OP)
AELLC,

Yes, that's exactly what I mean. However, in this case the "header" isn't a door opening; it's the opening for a garage, two cars wide, with two floors and a roof bearing down on it. The "header" is a steel beam and there is a 2' stud wall above it. I'm not involved in the project but I know people who are. I would like to provide them with a quick clean reference on the issue if such a thing existed. My understanding is that the state of Virginia used to specifically disallow it in their code but perhaps I'm wrong. I can't seem to find it in there now.

RE: Cripple Wall/Pony Wall Above Beam?

(OP)
Excel,

Yes, I agree. And this case seems to be well beyond something I would feel comfortable with. But, not being directly involved in the project there doesn't seem to be much I can do other than to suggest that the homeowner consult with the engineer of record, assuming there is one.

RE: Cripple Wall/Pony Wall Above Beam?

Archie264:
I don’t know if there is a prescriptive code requirement one way or another, but it is common sense engineering that you must pay attention to the fact that you might be introducing a hinge condition, and must design to account for that. There should be no problem taking vert. loads or lateral loads in the plane of the pony wall. And, that’s as far as most builders think of the problem. But, you have to take the lateral loads perpendicular to that wall another way. If we both have the same definition of pony wall, I’ve seen the problem more often as follows: a five or six course conc, blk. found. wall, with a 4' high stud wall on top of the blk. to the 1st. fl. framing. And, this produces a hinge at the mid height of the found. wall. Basically, the conc. blk. wall cantilevers from the footing to retrain soil pressure, or other lateral loads.

RE: Cripple Wall/Pony Wall Above Beam?

Usually the header (if in the low position) is designed for the vertical load and lateral load. Then the lateral load is transferred to the king posts, then to the diaphragm above/below.
I would also tend to agree with Excel that in general you don't see many issues either way.

I believe there was a post about which is the better detail a short while ago with some information. I'll see if I can find it.

EIT
www.HowToEngineer.com

RE: Cripple Wall/Pony Wall Above Beam?

For garage doors, you want the drop header so that there is capacity for wind bending normal to the header. However, a steel beam usually has much weaker Y-Y axis than its X-X axis, and with 2' of cripple wall above, there is some question about top flange stability against lateral-torsional. If you have the steel beam high, then the problem is bracing the top edge of the door opening against wind normal to the door (although the roll-up door doesn't transfer wind to the top edge).

Even with 2 floors and a roof, why can't a glulam or Parallam header calc out?

RE: Cripple Wall/Pony Wall Above Beam?

O.K.... given that AELLC’s sketches define the problem, the engineering logic would be the following: by putting the long steel beam right up under the fl. framing, you provide better lateral support for it (the primary load carrying member), from the fl. framing and diaphragm above. Then it feels a bit awkward to hang the 2' of cripple studs and a door header below the primary beam, but you still need some lateral strength/stiffness at the top of the door. If you sheath this entire detail with plywood or osb it should be just fine. When you put the steel beam right over the doors, you provide a good header with some lateral strength/stiffness, but the cripple stud/wood pl. on top of the steel beam does not provide good lateral bracing for the stl. bm. because of the of the hinge at the top of the beam. I’ll bet that was Virginia’s thinking on the matter. If you sheath this detail with plywd. or osb you end up with a plywd. box beam w.r.t.vert. loads, and a stressed skin panel resisting lateral loads and helping stabilize the stl. beam. The bigger problems, we now know, have to do with how this wall of the garage works as a shear wall, when 80% of it is door opening, and providing enough framing around the door opening and a strong enough door, so the door doesn’t just crumple inward in a strong wind.

RE: Cripple Wall/Pony Wall Above Beam?

(OP)
Thanks folks.

AELLC, as for using a glulam or parallam, well, it's not my project and I'm not involved. Someone asked what I thought of the configuration, which isn't much, incidentally. He seems to no longer be concerned so I'm backing out of it, other than for purposes of professional knowledge of the situation. I sure wouldn't design it that way but I don't suppose whoever's project it is much cares what I think about it in any case.

Thanks again.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close