Imbalance

Imbalance

Imbalance

(OP)

Small 120/240 Volt 3phase 5hp grinding pump that is triping on overcurrent.  FLA = 13.2 Amps/phase. The utility has a
voltage imbalance of 1.8%, but the current imbalance is 28%...Can anyone explain????

RE: Imbalance

Hi dpEng,

Whenever you get a problem like this it means more energy is being dissipated somewhere and the problem is finding out where. I don't like the imbalance in the currents but under overload conditions it's not a safe evidence of a motor fault. Have you tried running the motor without the pump. That's the easiest way of eliminating one half the possible causes.
Cheers
G

RE: Imbalance


Is the voltage balance the same at the motor terminals?

Search this site for “unbalance” or “imbalance.”  It has been extensively discussed here.  
  

RE: Imbalance

Suggestion: Check the motor windings.

RE: Imbalance

Sounds like you have a motor problem, but you could try rotating the phases as connected on the motor. Usually, there is a combination that minimises the imbalance. At light load, a small imbalance in supply voltage can result in a much larger imbalance in current. This has been discussed before. If the imbalance is occuring with the motor loaded, then you could have a shorted turn or similar.

Mark Empson
http://www.lmphotonics.com

RE: Imbalance

See FAQ's in this section. It talks about rolling the leads and discusses where this imbalance originates from. I think there is a definate problem with the motor or the wires going to the motor to have this much current unbalance. Good luck.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

White Paper - PLM and ERP: Their Respective Roles in Modern Manufacturing
Leading manufacturers are aligning their people, processes, and tools from initial product ideation through to field service. They do so by providing access to product and enterprise data in the context of each person’s domain expertise. However, it can be complicated and costly to unite engineering with the factory and supply chain. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close