Currant imbalance submersible pump

nj01

Agricultural
May 28, 2025
4
We have a 130kw submersible pump on a VSD that is showing nearly 9% currant imbalance. It also shows induced current on the earth rising from the motor.

The pump is 100m deep and the riser pipe is 8 inch and the well casing is 12 inch. Pump is 12 inch.

95 mm2 cable is run down to the 6 wire 130kw motor (three conductors up the riser, 6 out of motor).

Insualtion resistance starts @ 35mOhm and rises to 80mOhm

Winding resistance is .09 .09 .09 - so balanced.

From memory and would have to check , the DAR test was 1.1

We have tried all three hook ups and the imbalance follows the blue phase in each hookup.

Amps

212 185 208

voltage

r-w w-b b-r
449 450 444

Earth currant is 26a (3.5V) when connected to the well head imbalance is there, when disconnected imbalance is still there.



Any ideas on what is happening and how to fix?

Cheers

N
 
Last edited:
Replies continue below

Recommended for you

New motor?
New VFD?
New Cable?
or has it been different in the past?

New pump/motor and cable - existing vsd. we have no way of knowing if there was an issue with the old pump in terms of imbalance as the old paperwork from comission only noted drive amps as average of three phases.
 
It sounds like flat cable.
The inductive reactance per phase cable may not be equal.
We see that on long un-transposed distribution circuits.
The reactance per phase cable may not be equal.
I am taking a chance and assuming that you did roll the connections on the VFD.
 
It sounds like flat cable.
The inductive reactance per phase cable may not be equal.
We see that on long un-transposed distribution circuits.
The reactance per phase cable may not be equal.
I am taking a chance and assuming that you did roll the connections on the VFD.
We did not change the connections on the VFD, we assumed as the low current heading down the well that the issue was with the drop cables/motor or join.
 
This is a common problem.

When the pump was lowered down the well casing, the four conductors (three phase plus earth) need to be dead vertical and not rotate around the riser pipe.
If any one phase conductor is allowed to move around the riser by a partial turn, you will get a transformer effect inducing current into the earth conductor.
Typically in NZ, the earth conductor from the motor is bonded to the top of the well casing and this creates a shorted turn and induced current flows, but the induced voltage is very low.
I have seen earth currents as high as 120Amps and current imbalances as high as 20% at full load.
In extreme cases, we advise to lift the pump and be extra vigilent about how the cables go down the hole.

If the motor earth is bonded to the top of the well casing, and this is then earthed back to the supply earth bar, try running the earth from the motor directly back to the supply earth bar without connecting to the top of the well casing, and run a separate earth from the earth bar to the top of the well casing.
This has proved beneficial in some cases.
 
Flat cable or round?
Flat is a PIA since the inductance and capacitance is different for each conductor.
Here is a tip going forward, if you are running centrifugal pumps record the POWER for each phase.
 